Discuss optima xm6 prob with internal sounder going off. in the DIY Electrical Advice area at ElectriciansForums.net

Reaction score
5
optima xm6 alarm internal sounder has gone off and highlights tamper on the control panel. I have tested the battery with a multimeter which shows an output of 12v dc but i also tested the battery +ve and -ve leads off the board and that gave a reading of approx 11.08 volts dc. Is the battery (which is now 5 years old)on the way out or is the boards output not enough to cause a tamper fault on the board?
Thank you for your help
 
A few point to consider here:-

Your multimeter may not be as accurate as you think, I will assume been a DIY that you haven't splashed out a few hundred quid on it and get it regularly calibrated however.. for the response we will assume the multimeter is accurate as well as its batteries are not low.

A fully charged healthy battery would show around 12.6v +, if you are seeing 12v it would suggest your battery is on its way out or the charging circuit is failing, a fault on the panel or wiring also could drag the voltage down too so take that into consideration.
You definitely should replace the battery as a precaution and you'll be looking around 10-20 quid depending on its size, this may not resolve the issue but from experience some panels do go into tamper fault when the battery is duff so try it, batteries in alarms should be replaced every 4 yrs, it is a good idea to date the battery when you replace it so in future you can recall exactly when it was fitted.
 
  • Like
Reactions: DPG
As per darkwood.

Also, if this doesn't cure it then short out the tamper loop connections. If this cures it then you may have a fault with the tamper loop. Your multimeter, set to Ohms, will help find where it is.

Bell box tamper switches sometimes give issues.
 
A few point to consider here:-

Your multimeter may not be as accurate as you think, I will assume been a DIY that you haven't splashed out a few hundred quid on it and get it regularly calibrated however.. for the response we will assume the multimeter is accurate as well as its batteries are not low.

A fully charged healthy battery would show around 12.6v +, if you are seeing 12v it would suggest your battery is on its way out or the charging circuit is failing, a fault on the panel or wiring also could drag the voltage down too so take that into consideration.
You definitely should replace the battery as a precaution and you'll be looking around 10-20 quid depending on its size, this may not resolve the issue but from experience some panels do go into tamper fault when the battery is duff so try it, batteries in alarms should be replaced every 4 yrs, it is a good idea to date the battery when you replace it so in future you can recall exactly when it was fitted.
Thank you for the reply. I will start by changing the battery which is nearly 5 years old.
 
  • Like
Reactions: DPG

Reply to optima xm6 prob with internal sounder going off. in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi all Is it possible to connect a Texecom Odyssey 1E sounder to an Optima panel using 4 core cable and still allow the bell, strobe and tamper...
Replies
0
Views
764
Hello. I have an optima xm6 alarm system. Could someone tell me the best and safest way to check a battery fuse on the board. Do i need to turn...
Replies
0
Views
1K
Hi! Some help would be appreciated! I've just moved into new house, wanting to check insulation resestance etc as getting some nuisance...
Replies
2
Views
347
Hi everyone. The owner of the business I work for along with myself have created a DIY inverter setup that is giving us some issues. We bought...
Replies
4
Views
1K
All - Would appreciate some advise or professional help as I'm facing a £4.5K bill following an EICR which seems to highlight issues that passed...
Replies
21
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock