Discuss Overcurrent in circuits in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
39
Evening all...just a quick question. A customer was using a wallpaper stripper on a ring circuit, smoke started coming out of the back of the socket before the 32amp breaker tripped, what I don't understand is why the 13amp fuse in the plug didn't break? Could someone tell me why? Thanks
 
faulty socket or dodgy connection at the back of the socket, wires got heated, insulation melted and current sufficient to trip 32A went in.
 
Loose connection either in the plug, or at the socket outlet.

Possibly a too-small conductor for the steamer, though unlikely.
 
Steam cools,water acumalates behind socket,tracking between L+N or E ( no rcd) breaker current exceeded and out it goes
Plug top fuse intact because there is no excess current after the socket terminals
 
Fuses dont operate as fast as MCB's.
Now I dont have a BGB to see how fast a 32A MCB operates and at what current but Apparently a 13A Fuse is required to operate at 1.9 times rated current (24.7A) within 30 minutes.
So if its operating at say 40A it may take 15mins to blow where a MCB will probably operate faster.

Did you find what caused the fault?
 
Ive see temperatures in switch gear weld the terminals and cables yet the heat damaged HRC fuses don't operate..... the current needed to operate the fuse-wire needs to get it white hot, so in principle heat generated by a loose connection may not get anywhere near the same temp that is needed to melt the fuse wire.... when you've seen fuses glowing red without operating its an headscratcher the first time ....same principle applies with plug-top fuses.
 
Not sure what caused the fault, going to put it down to either water getting into the back of the socket or a fault in the wall paper stripper, tested the circuit and found nothing wrong.
 

Reply to Overcurrent in circuits in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I am using a 160watt-200watt multi uv tube stand alone sunbed,When the 2 power leads (plugs protected by 2x13amp fuses) plugged into a double wall...
Replies
9
Views
774
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi ive recently got myself a mig welder for my garage but each time i try to use it it trips out. Ive spoken to an electrician and he said its...
Replies
25
Views
809
Hello All, I am a homeowner (but not an electrician) and I am renovating a house that has an old CU containing MCBs and an MK LN5725 residual...
Replies
5
Views
855
Hi. I'm in the process of getting my qualifications and am taking on some small jobs for family to try and get some experience in. Today I was...
Replies
17
Views
871

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock