Discuss PAT testing 32A cable in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Reaction score
0
We have some 32A extension leads that range from 5m to 20m, I'm struggling to find what the acceptable values are for the resistence test. The PAT tester has a built in calculator, but that only goes up to 4mm cable, this is using 6mm. Where can I find the information I need to get the pass values to create my own test? Thanks.
 
This is from Code of Practice for In-service Inspection and Testing of Electrical Equipment. The list only goes from 1.25 to 2.5mm however one thing remains constant regardless of size and that is resistance, a quick calculation has them all at approx 0.18 ohm.
Length increases with csa and from this list this is approx ×10 of the csa so you could say for 6mm you have 60m to play with which also calculates to 0.18ohm.
Unable to load file but this is from the CoP
1.25mm -12m
1.5mm - 15m
2.5mm - 25m
 
We have some 32A extension leads that range from 5m to 20m, I'm struggling to find what the acceptable values are for the resistence test. The PAT tester has a built in calculator, but that only goes up to 4mm cable, this is using 6mm. Where can I find the information I need to get the pass values to create my own test? Thanks.
Get a copy of the ISITEE (PAT) CoP all the info will be in this publication.
 
resistance of 6mm @ 20deg.C. is 3.08 milliohms/meter. so you can workout the resistance of, say, 20m. i.e. 3.08 x 20 = 0.062 ohms. (to 3 dec. places).
 
Table 5.5 - Resistance per metre of copper conductors at 20°C for
---------------- calculation of R1 + R2
Conductor cross-sectional area
(mm²)
Resistance per metre run
(m ohms / m)
1.0​
18.1​
1.5​
12.10​
2.5​
7.41​
4.0​
4.61​
6.0​
3.08​
10.0​
1.83​
16.0​
1.15​
25.0​
0.727​
Note that to allow for the increase in resistance with increased temperature under fault conditions the values of {Table 5.5} must be multiplied by 1.2 for p.v.c. insulated cables (see {Table 8.7})
 

Reply to PAT testing 32A cable in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Similar Threads

Hi all, We have a limited in house PAT testing requirement and were advised that the TIS700 fitted our needs. The unit works fine for 110V and...
Replies
0
Views
674
The electrician that installed my cooker circuit put in 10mm cable with a 32a fuse, a 45a cooker switch and 10mm cable to the backplate for behind...
Replies
23
Views
892
Hello, I am currently learning and have come across PAT testing an old chandelier. On modern lamps I would use the plug and probe on the...
Replies
1
Views
2K
Hi all, looking for some clarification on MCB and cable sizes I need to run for a new kitchen. Cables will run through a combination of...
Replies
0
Views
3K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock