Discuss Plastic lugs on switch back boxes... in the UK Electrical Forum area at ElectriciansForums.net

J

j-lextricks

Morning comrades.
Is one obliged to change above back boxes for metal lugged versions. Obviously the plate screws won't be earthed but are insulated by plastic lugs. What are your thoughts? Thanks in advance.
 
Morning comrades.
Is one obliged to change above back boxes for metal lugged versions. Obviously the plate screws won't be earthed but are insulated by plastic lugs. What are your thoughts? Thanks in advance.
I would not think so,you get plastic lugs on dryline boxes,just earth the frontplate if its metal.
 
think you might struggle to get nylon faceplate screws into nylon lugs , nothing wrong with nylon lugs ,they insulate the face plate screws so better in my eyes , I would earth the back box mind , with this type of box there is not normally an earthing point , just a small lug you put the wire in and push it down what I do is to remove the fixing screw and put a ring crimp on the earth and screw it to the back box using the fixing screw
 
I think these were because until 1966 no earth conductor was installed in the switch drop so the back box would not be earthed the plastic lugs would insulate the screw on the plate from the metal back box Mk normally made these boxes used to see them a lot on council rewires and would normally lug an earth onto the fixing screw and reuse the box
 

Reply to Plastic lugs on switch back boxes... in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, I am an experienced DIY electrician and I just wanted to ask a quick question about something since I am new to this forum, if it hasn’t...
Replies
11
Views
1K
Hi, This post is about my concerns with medical IT socket outlets and want to alert you all if you are fitting them in a hospital. The current...
Replies
20
Views
2K
DIY question. I have been changing old metal socket faceplates to the normal plastic ones. All are working fine except the faceplate of a fused...
Replies
2
Views
991
Hi, Hopefully I haven't made an error but I was speaking with another electrician and he said standard junction boxes with screw terminals can no...
Replies
3
Views
865
I'm installing smart modules in my light switches which means I need to replace the existing 25mm back boxes with 47mm ones. Downstairs all walls...
Replies
0
Views
331

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock