Dish washer and washing machine on same double socket.
Definately not.

Regs may say yes. I say NO.

I would put good money on that socket will melt and burn out. Far too big a load on one double socket.

@brianmoooore spot on, bad practice. But I disagree with the “unlikely to cause problems”. My money is on melted socket.

as for it being a spur. That is not relevant. 2.5 mm cable will cope with the load. It’s the socket that won’t.

just my opinion.

guidance. And I repeat the word is “ guidance” recommends any appliance over 2 Kw should be on its own dedicated circuit.
 
Pirate's point is an important one. Spur (as I assumed), or spur off of a spur?
If I was doing the job, I'd fit 2 x 1G13A sockets in a dual pattress, but this technically means that one socket is a spur off of a spur (which is not allowed), while the overloaded 2G socket is.
Hi thanks for reply this is a single socket for for washing machine which is spur off ring maln assume I’m trying to get power to a dishwasher my only other option is a double socket which is supplying a hob ignition and a electric oven and swop for triple socket this again is a spur
 
Is the spur fused or unfused? I don't think we've discussed that. If it is fused this is not going to work at all.

If unfused, then it will work but as @Paignton pete points out, many double sockets will be at their thermal limit when both heating elements are on and might have a shortened life. While I agree with that, I think there is more chance of the individual plugs overheating due to their own bad contact and fuse dissipation, than due to the combined load of the two on one double socket. Provided the socket is a top quality one I would not worry as much as if one of the loads was a dryer. That would definitely be pushing one's luck.

my only other option is a double socket which is supplying a hob ignition and a electric oven and swop for triple socket this again is a spur

This won't work. 3-gang sockets are internally fused to 13A total because they are not 'single points' as per BS1363.

For my own purposes I would go with @brianmoooore's suggestion. Note however Pete's last point that you are clocking up some significant load on this ring (oven, washer, dishwasher) and if there are other large loads, (dryer, microwave), you have used up most of its capacity even allowing for diversity, when some of it really ought to be hived off to separate radials. OTOH, most of our house including all the above and a lot more ran on one 30A BS3036 for 30 years.
 
So you have a single socket, and want to make it into a double? If so, fit double pattress and a 1G socket in each.
As I wrote above, technically contrary to regs, but safe.
So you have a single socket, and want to make it into a double? If so, fit double pattress and a 1G socket in each.
As I wrote above, technically contrary to regs, but safe.
How do I screw both gangs in
 
New posts

Reply to Plumbing in a dishwasher and washing machine. in the Electrical Appliances Forum area at ElectriciansForums.net

Similar Threads

Wiring to new dishwasher causes garbage disposal to stop working. I just installed a GE dishwasher and came across a problem with the...
Replies
1
Views
707
Hi, I was just wondering if I have a dishwasher on a circuit of its own so I'm looking to put a double socket beside the fused spur in kitchen...
Replies
1
Views
1K
Sorry two questions today. We had the kitchen rewired based on existing units, but with a slightly new layout it puts the dishwasher right over...
Replies
1
Views
733
I have Curry's Essential tabletop dishwasher model CDWTT115 for nearly five years. Earlier this year my machine have stopped running during a wash...
Replies
0
Views
509
Hi all. So I'm designing my new kitchen and trying to plan where things will go. I currently have a 6 switch panel for the appliances (hob...
Replies
18
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock