Search the forum,

Discuss Possible Appliance fault tripping RCD in the UK Electrical Forum area at ElectriciansForums.net

AJshep

-
Esteemed
Arms
Reaction score
669
Just come back from an interesting fault.
Typical RCD tripping randomly. The customer was not using anything in particular, at any time.

Anyway I carried out Insulation Resistance on every circuit, each circuit was above 200M L-E and N-E and the
RCD tests were good.
The place was rewired in 2010 by a Domestic installer who did quite a nice neat job !!
I also removed the cover of the boiler to check for moisture and also carried out Insulation Resistance tests at 250v between L-E and N-E the readings were above 1M

Went round the kitchen carring out Insulation Resistance tests between L-E and N-E (only 250v just incase ) on the plugs for the Toaster, Fridge, washing machine etc.
Everything was above 200M

I'm the second spark to look at this and was just about to leave with my tail between my legs when the elderly customer mentioned that the last time it went she was talking to a friend on her laptop.

The laptop has recently been moved from upstairs to downstairs and is plugged in to a socket constantly turnned on and charging all the time because the plug is a little hard to get to.

So I got my test kit out and tested the IEC type lead that plugs into the Power supply

L-E 0.17 Mohm
N-E 0.26 Mohm
Obviously not good, and ive told the customer to get a new one, and not constantly charge her computer.

it's been disconnected all day because another member of the family went round earlier to unplug stuff to see if they could help. Has anyone ever had this before ?

I'm thinking as the lead gets warmer the fault gets worse causing the RCD to trip.
 
The appliance wasn't or has never previously been PAT tested as such, I just used my Insulation Resistance tester on the plugtop one clip on the Earth the other on the L or N pin.

Yeah I know most things would just trip the RCD but using ohms law 0.17M still isn't quite enough to trip a 30mA RCD.

That's the annoying thing :(
 
Last edited:
I often find that the readings measured (normally on circuits) are higher than would be necessary to trip an RCD but the RCD still trips!
Cheap IEC leads often have poor connections but at the sort of reading you are getting I would suspect the lead got wet at some point, it does not seem to be a near copper to copper contact, possibly if water is inside the cable sheath the slight warmth of running will allow it to migrate to the terminals.
However this is all supposition and changing an IEC lead is much easier than defining the fault, if it works, then problem solved.
(What a bad approach to testingo_O).
 
I had one the other day customer saying she had a tingling every time
she use the dish washer, opened the sink cupboard up ,holly f88k ,the appliance engineer put a moulded plug on a extension lead .and the washing liquid all over the plug and the extension lead ,the customer said he could not put the moulded plug in the socket under sink .
fixed the under the sink .
got a call same customer ,the dishwasher having tingling off it .
pat tested it . failed the pat test .told her, she said it worked .yeah .
blaming me for F.F faulty dish washer . I could have put her head in the F.F dish washer .pratt
 
That's how I've left it with the customer, the customer is happy but it's always satisfying to have a clear cut answer !

the lead is an original but I assume the conductors are pretty small, I can't find a pic of the lead to show everyone but it's like an IEC lead, the comnection end is more rounded though a bit like a 3 leave clover !
 
Damage to laptop charger cables like this is very common, because people regularly wind the cables around the charger block very tightly and this eventually damages the flex cable, another common fault is the laptop charging pin/socket on either the laptop or the lead gets damaged causing a short circuit.
 
I have never had an IEC lead fail an IR test no matter how much it has been deformed, earth continuity yes with Chinese imports. As in #4 I could only put it down to water ingress.
 
What's the background leakage across the property?
Well intailly i would have said pretty low !
I got readings of greater than 200M on all of the circuits.
However when I carried my Insulation Resistance tests I had everything unplugged, it was only once I had confirmed that circuits were clear that I started looking into appliances.

I'm always a bit dubious of carrying our IR tests on appliances that's why I step my meter down 250v and only Test between the Lives and Earth.

My initial thought was the boiler as it was one of the things that would be running all the time when I carried out An IR test on the boiler itself (250v on Lives -Earth) I got around 1.07M ohm so I suppose theres two resistances I should parallel up, then when you factor in other equipment that I did not test the background leakage could infact be the tipping factor.
 
Sorry Murdoch,
I completely misunderstood !
Yes I have however I had no access to it at the time (saturday) as its locked up at work.
Just had my hand tools and my MF testkit.

That would have given a nice starting point !
 
I can see the logic of that. I expect that saves a bit of time. If I'm honest it wasn't something that initially sprung to mind.

Im going to have to buy a new one anyway, In a couple of weeks.
What's the scale on yours ? think the one at work lowest is 200mA
 
I've had boiler pumps causing havoc with RCDs before. But if it was that, it should trip when it tries to run. Does the boiler have an internal pump? If so, it's possible that it wasn't in circuit when you were IR testing perhaps.
 
I've had boiler pumps causing havoc with RCDs before. But if it was that, it should trip when it tries to run. Does the boiler have an internal pump? If so, it's possible that it wasn't in circuit when you were IR testing perhaps.

The Boiler was a Combi boiler ( again less than 8 years old ) with an external potterton 1 channel time clock for the heating.
So when I carried out a Insulation Resistance test i doubt the pump would have been included in the circuit.

If the problem remains I'll stick the link back into the boiler.
To be honest there wasn't a great deal on effected side of the DB.

Upstairs Lights ( no outside lights)
Downstairs Ring ( no outside sockets)
Boiler ( 1 x twin socket in loft, with a TV amp also plugged in)
Smoke Alarms ( 3x Aico, interlinked )

But the boiler has been running pretty much all the time keeping the house at a constant 20 degrees.


ACAD126G.jpg

By the way here's a pic of the damaged lead !
 

Reply to Possible Appliance fault tripping RCD in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys. Having a weird problem in a house that has suddenly happened. One half of the ring main has 240ish volts (fluctuates of course), and...
Replies
9
Views
516
So was on a call out today and cooker circuit kept tripping the RCD. Disconnected at the board and at the cooker switch and IR’d the cable and...
Replies
9
Views
441
Recently changed a CU for a friend and today when visiting one of the RFC's RCBOs tripped. It was due attention anyway as open ring and no time to...
Replies
13
Views
1K
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
872

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock