Discuss power fed light switch Hager rcbo won’t trip in the UK Electrical Forum area at ElectriciansForums.net

Just a thought, I worked for a long time as a spark and AV engineer in the entertainment industry and some of the dimmers for LED stage lighting in that sector that I came across had fully isolated outputs. I haven't come across that in a domestic install personally though, but could it be????
 
depends what part of the cycle you are testing.
some dimmers are leading edge and some are trailing edge.
have you tried testing RCD on both positive and negative cycles?
most hager RCBO will trip within 1 cycle (20ms) regardless of testing at 0deg or 180deg.
 
Wait, are you connecting your RCD test meter to the output side of the dimmer? I'm surprised the meter isn't complaining about the rough supply.
 
Are you testing it as an AC setting on MFT, as an A-type test, some testers do not have a variable test current to test correctly?
What tester are you using? Is any DC earth leakage present which may influence the result?
 

Reply to power fed light switch Hager rcbo won’t trip in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have an issue with a home lighting circuit 6A RCBO provides power to 13 bulbs which randomly keeps tripping, when I say randomly it keeps...
Replies
8
Views
3K
Hi all, Wondering if you could offer some advice please. I carried out a small outdoor lighting project today at a commercial property. 4 lights...
Replies
5
Views
970
So here is the thing Rhere is an old MEMSHIELD TPN+E Board that is pretty mich obsolete. The only place that sells their breakers would be Ebay...
Replies
5
Views
896
Ring main was on a c40 rcbo so I tested the circuit everything was fine and dropped down onto a b32, It’s quite a long circuit but only serves...
Replies
26
Views
2K
Hi all Now being upfront I am not a sparks. I am about to have some work done by a friend (certified) and as he is doing me a favour I want to as...
Replies
5
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock