Hi, I'm new here and looking at this True Sine Wave Power Inverter from AliExpress, but I have never seen any inverter without a transformer?
How do they work without one, and how does this one's build look for a cheapish China one? (£125)
As I'm not abele to spend much money as it's to power a 75w 240v fridge with a 900w start up load (30 seconds), a small 600w kettle and a microwave oven with a 1400w peak load, the kettle and oven won't be run at the same time, and the power for the inverter is coming from a 400w panel and 300ah of Lb batteries all in a garden shed on an allotment.

Also, I just had to return another inverter I got off ebay that was claiming to be a true sine wave, but I soon found out it was a modified wave which made the fridge loud as hell.

So please feel free to tell me what you think.

Aaron.
inverter 2500w5000w.PNG
 
The transformer is the toroid labelled 'amorphous inverter.' The heavy leads in glassfibre braid form the primary and the enamelled copper wire the secondary. It runs at such a high frequency that very few turns are needed and the core area is very small.

I think the rating is probably a little optimistic, it's quite lightly built, but impossible to tell with any certainly how it will last or perform. The devil is in the detail - e.g. capacitor ESR and lifetime, transistor rating, design of the bridge driver - which can only be guessed at without measurement and testing. I can see things I would design differently.
 

Reply to Power Inverter Without a Transformer? Please Help in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

J
Hi Recently purchased something called a Paceman Pro Bowling machine. The manufacturers have not yet come up with their own portable power...
Replies
2
Views
11K
D
Hello everyone, so i'm trying to build a 12V to 240V power inverter with a 2 Transistors a tenter tapped step up Transformer and a Microcontroller...
Replies
1
Views
1K
RobWansbeck
R
R
Five days without solar but guess I haven’t missed too much yet, thanks to the grotty weather. I’ve had my solar installation since June 2011...
Replies
29
Views
4K
iconnect
I
U
Hello I require some help. I have a solar system I have built myself, I have 4 *80w panels wired in parallel which connects to a 30A MPPT...
Replies
2
Views
2K
UKGadgetMan
U

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock