Discuss Power to an Outside Office - Spur from Ring Final? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Marcus Vaughan

-
Esteemed
Reaction score
240
Hi All,

Just looking for some reassurance on a job I've looked at today. My status is that I am trying to stay within the realms of 'Minor Works' until I get a bit of experience under my belt. Conscientious decision - but everywhere I go it seems that notifiable work is needed as well. Anyway......

So - a customer has asked me to supply power to an outside office that's about to be built (when it stops raining), and has asked if I can take the supply from a nearby external supply he has spotted (actually supplies a pond). I've done my homework, read around the subject.

TNCS
Pond Supply = 2.5mm but spurred from B32 Ring Final.
Tested (live) Zs near the pond at 1.28 ohms so already a bit naughty.
Ring Final IS RCD protected.
The outbuilding has no extraneous conductive parts.
Not sure on the demand for the office but its pretty small, it has its own 'garage unit' (apparently) so suspect a B16 for sockets and B6 for lights.
New building is a gnats whisker from the man house and ring final.

It needs a new circuit - doesn't it?

I'm clutching at straws because the consumer unit is a long way from the new building, and running a new circuit will be a fair amount of work for a few sockets and a light.

I'm toying with taking another fused spur from the same ring (if Zs is low enough), through the walls and into the new building.

What then though - I understand you need a double pole isolator in the new office - but do I ignore the 'garage' consumer unit or use it? Maybe run a 4mm from the house ring final spur to the garage unit? Not ideal, but if Zs (or Zdb) in limits at the garage unit.....

I'll be interested to hear your thoughts and opinions.....
 
If you are going down this route then just make sure you state the max 13A supply in your quote and explain this to the customer.
Got to C.Y.A. if the customer decides to put 3 heater into the place then whinges..
Are the cable calcs ok for Zs and other rubbish?
 
It's the cable calculations I'm looking at now. It's a bit close to the mark with the B32. It's probably best if I do dead tests instead of live Zs Tests through the main board RCD...

I like the idea of stating the max 13 amp. on the quote though. Makes sense.
 
suspect a B16 for sockets and B6 for lights.
If you are running the supply from a 13A FCU, then what is the point of this second CU?

You won’t get any discrimination, and the source ring final is already RCD protected, so you don’t need another one!

This needs a separate circuit. Sorry if this is outside your experience/ability.
Park it and walk away.
 
Yes. I’d say so. Biggest demand likely to be the heater.

Can’t see the 13 amp fuse blowing in the spur...
I'd say there is every chance of the fuse blowing. Heater/PC/Printer/TV/Fridge/Vacuum Cleaner etc etc.

Also I find modern Fused Spurs (of pretty much any brand) are pretty garbage if anything like 2-3kW is the load for long periods of time
 
Yeah. I might give the customer a choice.
60 metres of SWA and labour (and an RCBO)
Or 4metres of Twin and Earth.
I wonder what they'll go for?

Hold on ................ 60m of SWA or 4m of T&E ................ can you explain

And I would NOT be recommending anybody that they try and run a garden office off a 13A spur......................
 

Reply to Power to an Outside Office - Spur from Ring Final? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Bit of advise if anyone has time.. I have a customer who brought a new kitchen from wrens. Customer has had the route to the kitsch redecorated...
Replies
3
Views
1K
I have supply in the garage with its own small consumer unit with a 63a breaker and 1 B6 and 1 B16 breakers. The garage has a ring of sockets...
Replies
2
Views
994
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hi Guys, Long time member and not a regular user here. I do pop in here when the odd unknown pop's up and unable to locate an electrical dilemma...
Replies
4
Views
901

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock