Hi, this might be an easy question, but i need to power a single phase motor situated about 300 meters away from my MCC. Do I just run 3 phases 415VAC cable to the motor in the field and just connect one live phase and the neutral to get the 240VAC? if that's the case then what do I need to do with the other remaining live wires at the motor location? OR do you I need to modify the MCC and run 240VAC from the MCC to the motor? beside the neutral is earthing cable needed at the pump too?
 
I don't understand your question if earthing cable is required at the pump. If it's a steel wire armoured cable you're installing the cable armour needs to be earthed. Most pumps require a CPC (an earth) so I would provide one in the pump supply even if it's not used. Single phase pumps from an MCC are unusual because it makes load balancing and effective PFC difficult. I'm assuming this is a small pump? Personally I'd probably run a 4 wire and earth cable and double up on the 2 load wires also sleeving and ID'ing them appropriately to give a future option for any replacement pump in future to be 3-phase.
 
Hi, this might be an easy question, but i need to power a single phase motor situated about 300 meters away from my MCC. Do I just run 3 phases 415VAC cable to the motor in the field and just connect one live phase and the neutral to get the 240VAC? if that's the case then what do I need to do with the other remaining live wires at the motor location? OR do you I need to modify the MCC and run 240VAC from the MCC to the motor? beside the neutral is earthing cable needed at the pump too?
I can't see any point in running a 3 phase supply all the way to the motor when you can get away with a suitably sized 3 core swa
If you're going to maybe use a 3 phase motor in the future then as above
 
Last edited:
Welcome to the forum mate.

Also the volt drop on 300 meters is going to be quite a bit, so from a cost point of view 3 cores will be a lot cheaper.
 

Reply to Powering single phase motor from 3 phases in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

Absolutely losing my brain here guys What I would like to be able to do is power our 3 phase motor on a single phase supply. Thought I had it...
Replies
3
Views
674
Hi, I am looking for a connection diagram or sugestions for a 2.2Kw single phase motor to drive a compressor. The spec plate shows that it can be...
Replies
5
Views
787
I have been asked if I can wire a motor for a car lifter in a domestic garage, however the motor is 3 phase and only single phase is available in...
Replies
5
Views
828
Hi Guys, We have a CNC router which uses single phase for the spindle, stepper motors and control box. This is all wired in and working...
Replies
10
Views
1K
Hi All, I have recently purchased a motor soft starter from aliexpress for a 3 phase motor Before connecting load I measured the input and...
Replies
0
Views
349

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock