- Reaction score
- 5
Morning,
Company had an external contractor coming in to complete an EICR recently. They have gave us the report with a C2 for holes in trunking at high level. For reference, this trunking has been pre-drilled with 20mm holes at set distances on either side. Within this trunking is multiple single core and multicore cables but no live parts. Personally, I think it's overkill but not had a lot of experience with test/inspection coding.
The main tester on site has also recently became director of the company so I may be thinking cynically that he was merely trying to provide easy work for his business
Company had an external contractor coming in to complete an EICR recently. They have gave us the report with a C2 for holes in trunking at high level. For reference, this trunking has been pre-drilled with 20mm holes at set distances on either side. Within this trunking is multiple single core and multicore cables but no live parts. Personally, I think it's overkill but not had a lot of experience with test/inspection coding.
The main tester on site has also recently became director of the company so I may be thinking cynically that he was merely trying to provide easy work for his business