Morning,

Company had an external contractor coming in to complete an EICR recently. They have gave us the report with a C2 for holes in trunking at high level. For reference, this trunking has been pre-drilled with 20mm holes at set distances on either side. Within this trunking is multiple single core and multicore cables but no live parts. Personally, I think it's overkill but not had a lot of experience with test/inspection coding.

The main tester on site has also recently became director of the company so I may be thinking cynically that he was merely trying to provide easy work for his business
 
A bag of 20mm blanking plugs will sort it. Easy fix
dont even need to open the trunking.
https://www.NoLinkingToThis/p/deta-closed-grommets-20mm-100-pack/884vt

Access to single insulated cables without the use of a tool. Oooh I'm in a mischievous mood today:)
 
Access to single insulated cables without the use of a tool. Oooh I'm in a mischievous mood today:)
Would that mean any consumer unit with plastic push in blanks is not compliant ? Or a wago jb.
 
Would that mean any consumer unit with plastic push in blanks is not compliant ? Or a wago jb.

Wago JBs should have a cable tie fitted through the loop provided. This needs cutters to remove it.
 
Wago JBs should have a cable tie fitted through the loop provided. This needs cutters to remove it.
I maybe wrong, but I think that's only when used MF there are many junction boxes that have clip on lids, but wouldn't be compliant for inaccessible locations
 
Last edited:
I maybe wrong, but I think that's only when used MF there are many junction boxes that have clip on lids, but wouldn't be compliant for inaccessible locations

No, you can use the cable tie feature any time you use a wago box, regardless of whether you need it to be MF or not. And then it needs a tool to open it.
 
No, you can use the cable tie feature any time you use a wago box, regardless of whether you need it to be MF or not. And then it needs a tool to open it.
You MUST use the tie to be MF compliant, but you don't have to use it when used in accessible areas.


DPG said:
Access to single insulated cables without the use of a tool.

As already said, there are many Junction boxes that can be opened exposing single insulated cables that can be opened without the use of a tool, including single push in blanks in a DB.
 
You MUST use the tie to be MF compliant, but you don't have to use it when used in accessible areas.


DPG said:
Access to single insulated cables without the use of a tool.

As already said, there are many Junction boxes that can be opened exposing single insulated cables that can be opened without the use of a tool, including single push in blanks in a DB.

I was just replying to your example of a wago JB not needing a tool to open it.
 
Access to single insulated cables without the use of a tool. Oooh I'm in a mischievous mood today:)
Would someone be so kind as to give me a Reg No. for this?
 
"521.10.1
Non-sheathed cables for fixed wiring shall be enclosed in conduit, ducting or trunking.
Non-sheathed cables are permitted if the cable trunking system provides at least the degree of protection IPXXD or IP4X, and if the cover can only be removed by means of a tool or a deliberate action."

The last bit about deliberate action is a little vague in its intent...
 
"521.10.1
Non-sheathed cables for fixed wiring shall be enclosed in conduit, ducting or trunking.
Non-sheathed cables are permitted if the cable trunking system provides at least the degree of protection IPXXD or IP4X, and if the cover can only be removed by means of a tool or a deliberate action."

The last bit about deliberate action is a little vague in its intent...

Good find. Cheers!
 
I hadn't come across IPXXD before. From a quick Google it seems a way of establishing safety by testing - using a probe 1mm dia and 100mm long and checking it cannot come into contact with live parts. As stated, single insulated cable is not regarded as a live part.
It seems a bit extreme to poke a probe into every hole in a completed length of trunking, but doing a sample would be one way of demonstrating the trunking is compliant (that is assuming the trunking has a cover requiring a tool to remove)

I think there's grounds for challenging the C2, unless I've missed something 🤔

From Voltimum (so it must be true 🤪):-

IPXXD:

For this degree of protection, only the third letter ‘D’ is relevant. The letter ‘X’ signifies that the first and second letter protection levels are not specified. BS EN 60529:1992 + A2:2013 states the requirement for ‘D’ as the degree of protection required for protection of persons against access to ‘hazardous parts’. An access probe having a maximum diameter of 1mm and maximum length of 100 mm, when inserted into any gap or joint within an enclosure with an applied force of 1 Newton, must not make contact with ‘hazardous parts’.
 

Reply to Pre-drilled holes in trunking EICR Code in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Recently visited a new build to do a very minor job and spotted a few dodgy looking items so Client asked me to do an EICR. Following items I...
Replies
6
Views
977
I commissioned an EICR to be done on a property that is in Wales as this is now a requirement in order to let on any new tenancies after 1st...
Replies
1
Views
2K
Morning all So the site I'm based at recently had some work done (think partitioners). This package of work included electrical. This was...
Replies
47
Views
8K
My wife is on the committee of the local village, and they have just had an EICR carried out. This came out as 'unsatisfactory' and accompanied by...
Replies
14
Views
3K
Hi, Recently I had solar panels fitted and realised how they have done it and I hope someone will be able to give me advice how bad and dangrous...
Replies
16
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top