Discuss Problem this afternoon in the UK Electrical Forum area at ElectriciansForums.net

When you say first point , what is that showing a re all 3 cores o/k to that point , and its what happens to it after that to the j/b is that right ...
 
I would be inclined to run out a new supply to the j/b and ditch whatever is before that , then think about refeedng the other points after that ,,
 
I dont think I have made myself very clear...

the junction box is not the first point, but it is the nearest point to the CU at only 2.5m away. It is the radial with the boiler cut into it.

The nearest point / socket is approx. 12m away, I presume this is the first point as it has the lowest resistance on the line conductor compared to all of the others.

One thing I could do, but not too sure if its such a great idea, is just disconnect the feed from the CU and just run a new leg up to the junction box as I know everything has continuity from that point, but this would leave the bad leg in place and live.

How would you feel about doing that? Ok its the easiest quickest way but does it comply? it would not be a radial, but more of a lollipop shape...
 
Hi,

Just popped back with the new tool Martindale CD1000, found the problem within 30 mins.

this is a downstairs plug circuit bare in mind.

Upstairs socket in one of 5 bedrooms, he had changed a LOT of faceplates round the house, anyway, one socket in a bedroom, three cables into it for some reason, so a random socket with a spur coming off it i guess, anyway, jist of it is, one of the neutrals had not been connected, it was sitting at the back of the back box....

DAMN DIYER'S!!!

But the CD1000 foudn it as it was squealing away then it stopped, worked a treat and without it i would have literally had to remove any faceplate.

Problem solved
 
Hi,

Just popped back with the new tool Martindale CD1000, found the problem within 30 mins.

this is a downstairs plug circuit bare in mind.

Upstairs socket in one of 5 bedrooms, he had changed a LOT of faceplates round the house, anyway, one socket in a bedroom, three cables into it for some reason, so a random socket with a spur coming off it i guess, anyway, jist of it is, one of the neutrals had not been connected, it was sitting at the back of the back box....

DAMN DIYER'S!!!

But the CD1000 foudn it as it was squealing away then it stopped, worked a treat and without it i would have literally had to remove any faceplate.

Problem solved

It's easy with the right tools in the armoury
 
New posts

Reply to Problem this afternoon in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Today I was doing an EICR and went around a couple sockets with a Megger MST220 socket tester just to see if there was anything obvious, all three...
Replies
20
Views
682
Hi. I'm in the process of getting my qualifications and am taking on some small jobs for family to try and get some experience in. Today I was...
Replies
17
Views
817
Hi guys. Having a weird problem in a house that has suddenly happened. One half of the ring main has 240ish volts (fluctuates of course), and...
Replies
9
Views
480
i have just started my course as a trainee electrician...some advice on the following will be appreciated: I have a spare 16 and 32A MCB (RCD...
Replies
5
Views
204
Hi All, I own a country Villa out in the Spain countryside. Was having problems with water pressure so local tradesmen advised to get a water...
Replies
14
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock