Hi,

Got called to a customer today, background is he has been doing some DIY... he had replaced a load of light fittings and plug sockets, he said we extended this one here and burried it in the wall etc... found one twisted together with tape, no connectors etc... anyway..

The problem is, since yesterday, he said the plugs downstairs don't work... hmmm

I plugged the socket tested in, beep beep beep beep beep, Earth and Live Reverse.... so i go to another, and get the same, then go to another, and its already beeping at me without switching the switch on, its a Fluke socket tester, first two are lit up, then switch it on then its just the first one so suggest Live earth reverse.

I then get the MFT out, plug it in at a socket,

Line to Neutral = 5.5v
Line to Earth = 230v
Neutral to Earth = 230v

Hmm, that's not right...

I pulled off all the face plates down stairs that I could that appears to be on that circuit one at a time thinking ill find the problem, but nope, nothing, all seemed in order (a mess but in the right holes). They said they did not extend or chop any circuits on the plugs, only the lights (they work fine).

Oh its a radial by the way.

So then the lounge, I took the faceplate off, left all conductors hanging (terminated in wagos) turned back on, same problem on sockets, but the ones he had changed were all dead, so im thinking must be somewhere else, put it back together.

Looked at the consumer unit, dual split board, a mess, blatant cowboy who fitted it, everything in the wrong places etc, but anyway, RCD protected. So the circuit was holding fine, as was the RCD.

I put a jumper between Line and Earth and then went round the sockets to get an R1+R2, all seemed pretty much in order, went round everything I could find, all seemed to be ok.

Then hooked Line to Neutral, went round the sockets, not a bloody sausage, nothing, not on any socket anywhere, nothing hooked off the circuit.

Then hooked Neutral to Earth and got a reading on everything.

So then I thought, well everything appears to be in the correct places so what the hells going on... I said it Friday night, I want to go home now thanks, and am going back next Tuesday and have left the circuit off.

My next step is to remove all faceplates on the circuit, so perhaps 15 say, then try to connect one at a time and see what happens.

Has anyone got a better suggestion as ill be honest, im stumped on this, I normally find these things quick and move on, but I spent 2.5 hours then this evening and couldn't work it out.

He assures me he has only changed Faceplates, only 4 of them down stairs in the lounge, you could see they were new. He has not touched anything else on the plug circuit.
 
Hi,

Got called to a customer today, background is he has been doing some DIY... he had replaced a load of light fittings and plug sockets, he said we extended this one here and burried it in the wall etc... found one twisted together with tape, no connectors etc... anyway..

The problem is, since yesterday, he said the plugs downstairs don't work... hmmm

I plugged the socket tested in, beep beep beep beep beep, Earth and Live Reverse.... so i go to another, and get the same, then go to another, and its already beeping at me without switching the switch on, its a Fluke socket tester, first two are lit up, then switch it on then its just the first one so suggest Live earth reverse.

I then get the MFT out, plug it in at a socket,

Line to Neutral = 5.5v
Line to Earth = 230v
Neutral to Earth = 230v


Hmm, that's not right...

I pulled off all the face plates down stairs that I could that appears to be on that circuit one at a time thinking ill find the problem, but nope, nothing, all seemed in order (a mess but in the right holes). They said they did not extend or chop any circuits on the plugs, only the lights (they work fine).

Oh its a radial by the way.

So then the lounge, I took the faceplate off, left all conductors hanging (terminated in wagos) turned back on, same problem on sockets, but the ones he had changed were all dead, so im thinking must be somewhere else, put it back together.

Looked at the consumer unit, dual split board, a mess, blatant cowboy who fitted it, everything in the wrong places etc, but anyway, RCD protected. So the circuit was holding fine, as was the RCD.

I put a jumper between Line and Earth and then went round the sockets to get an R1+R2, all seemed pretty much in order, went round everything I could find, all seemed to be ok.

Then hooked Line to Neutral, went round the sockets, not a bloody sausage, nothing, not on any socket anywhere, nothing hooked off the circuit.

Then hooked Neutral to Earth and got a reading on everything.

So then I thought, well everything appears to be in the correct places so what the hells going on... I said it Friday night, I want to go home now thanks, and am going back next Tuesday and have left the circuit off.

My next step is to remove all faceplates on the circuit, so perhaps 15 say, then try to connect one at a time and see what happens.

Has anyone got a better suggestion as ill be honest, im stumped on this, I normally find these things quick and move on, but I spent 2.5 hours then this evening and couldn't work it out.

He assures me he has only changed Faceplates, only 4 of them down stairs in the lounge, you could see they were new. He has not touched anything else on the plug circuit.

There's your answer Earth to neutral 230 volts you've lost a neutral some where and confirms it with live earth reverse on a socket tester not an accurate means of testing
 
Well yes, ill be getting the wander lead out when I go back, I hadn't really got time to look to far into it as its Friday night and ive got better things to do live go on here LOL.

I will do as in post #4

Surely if you are getting 230v across Neutral and Earth, how can you have a lost neutral? Clearly there is one there as its got 230v across it.

Not only that you shouldn't get 230v across Neutral and Earth, so how do you explain that if the Neutral is lost?

Also, if you are saying its a lost neutral, how comes you don't have 230v from Line to Earth?

I tested this with my MFT to see, it clearly showed:

Line to Neutral = 5.5v
Line to Earth = 230v
Neutral to Earth = 230v

This is not readings from a socket tester. I only plugged the socket tester in to see if it was 'normal' so to speak. If you had no neutral you would not get 230v Neutral to Earth.

Am i being thick and missing the obvious or something?
 
No there's 230 volts to earth, meaning the neutral is not returning to the DB and beyond. As others have said wander lead test every cable.
 
New posts

Reply to Problem this afternoon in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Today I was doing an EICR and went around a couple sockets with a Megger MST220 socket tester just to see if there was anything obvious, all three...
Replies
20
Views
758
Hi. I'm in the process of getting my qualifications and am taking on some small jobs for family to try and get some experience in. Today I was...
Replies
17
Views
877
Hello everyone, Hope you're all well. I'm carrying out an overall/global insulation resistance test on a newly wired 3 phase installation we did...
Replies
24
Views
1K
Hi guys. Having a weird problem in a house that has suddenly happened. One half of the ring main has 240ish volts (fluctuates of course), and...
Replies
9
Views
509
i have just started my course as a trainee electrician...some advice on the following will be appreciated: I have a spare 16 and 32A MCB (RCD...
Replies
5
Views
309

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock