trevormbush

Ive installed an additional RCD onto an existing Wylex board that already had one RCD, however a breaker on the old RCD circuit is tripping the new RCD and for the life of me I cant figure out why. Anybody have any ideas?
 
Did you install a separate neutral bar for this additional RCD?
 
You have either a borrowed/crossed neutral on one of the circuits or you have neutral(s) in the CU crossed between the neutral bars.

Did you test all the circuits before you split them across the two RCD's?
 
Come across similar. Turned out liggts had been split upstairs and downstsirs but the upstairs lights had borrowed a neutral off the downstairs lights
 
Come across similar. Turned out liggts had been split upstairs and downstsirs but the upstairs lights had borrowed a neutral off the downstairs lights

I want to know why and how the 2nd RCD has been added....... unless the OP answers us we are pxssing in the wind.

He's online so heres hoping for a response....
 
There was originally an RCD on the board but for whatever reason the previous owner of the house (a self confessed DIYer) had taken the RCD out. My initial thinking is the same as chopper that there is a borrowed neutral somewhere else.
 
I should have also mentioned that I tested all the circuits before adding the additional RCD and they worked fine. I have also checked and all the neturals are split correctly. Each line has its own netural which is in the correct place. Im thiking Im going to rebuild the board just for my own sanity.
 
Sound like simple borrowed neutral to me. Try narrowing it down by putting both lighting circuits together and see if it trips then. If it doesnt then probs borrowed neutral on the landing/stairs. If not try the same for both sockets circuits.
 
obviousy the home owner had the same problem, and that,s why he removed it. i'd first check where the L to the 2 way landing light comes from. you could try putting both light circuits on the same RCD. if it don't trip then, that's your answer.
 
Ok. Which circuit do you think might be causing the tripping.................................................................................

This is like pulling teeth.
 

Reply to Problem with RCD tripping in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
342
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
1K
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
806
I have a client with what appears to be an intermitent fault on the lighting, but trips the power. The installation has a 16th edition board with...
Replies
17
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock