Hello professionals out there! This is my first question on this forum.
I am not a professional and have no electrical qualifications.
I have a PV and battery system. The battery was installed in 2016 and is still under guarantee. It is a Samsung 3.6 KW in the A10 series. Samsung have now stopped that side of their business and have passed it over to Hansol (who apparently made the thing for Samsung in the first place). It was installed by Avonside Eco Homes, which was a subsidiary of Avonside Roofing, but is no longer trading.
Recently, the battery system has started randomly shutting itself down. Switching it off at the main isolator and on again resets it, when it will run again for random amounts of time - it could be a minute or two, or some hours or even all day.
I contacted Hansol's service department, who monitored it remotely through its internet connection and said that over-voltage on the grid was causing it to trip. They said it is set to trip in excess of 253 volts. I contacted Western Power Distribution, who thought this unlikely, but fitted a monitor to record voltages continuously for a week. During that time the A10 continued to trip randomly, but the grid voltage never went higher than 245.8.
In the meantime, I had noticed that the system only tripped when the Immersion controller was set to automatic. Ours is an Absolute Energy Master, and was installed by Avonside as part of the package that came with the battery. I pointed this out to Hansol, who said that they didn't know what that was (although I told them) but that the A10 is not designed to run with one. Absolute Energy have now gone out of business, so I cannot pursue that line. Avonside now have nothing to do with batteries, only PV panels, and Avonside Eco Homes no longer exists, so no joy there either.
My suspicion is that the immersion controller is not to blame, as I have two - the other is running a heater in the hall (only used in winter, when the hot water is produced by a back boiler in an Aga, which we turn off in summer and use an immersion heater). I have tested the second one, and the A10 trips randomly with that too. It seems unlikely that both would fail in the same way at the same time. Also, much more recently I have noticed that if I don't switch the immersion controller on (i.e. to automatic) until the battery is nearly fully charged (85% or more), then the system does not trip, but works perfectly, with current fluctuating correctly with the level of sunlight and other appliances being used.
So, if anyone has managed to plough their way through this and got to this point, do you have any ideas about what the cause of this might be and whether I can get anything done about it?
 
Hi - never fear, several of us have read through it all now :) . Doing my very simple logic on the problem - either there is an overvoltage and the unit correctly trips, or there is not an overvoltage and something else makes it trip but it (incorrectly) reports the fault as overvoltage. It might be interesting if you can create a trip by manually operating the immersion controller (?).
 
Could you also provide me with make and model of your immersion heater controller?
The controller is an Absolute Energy Master and I attach a copy of the installation Guide, which gives some technical details. They have now gone out of business, so the contact details on the back page lead nowhere.
The photograph on the front page of the installation guide is of the monitor, which is near the consumer unit and meters etc for ease of attaching the current-sensors to the relevant cables. The screen is touch-sensitive and is how the various settings are made - e.g. touching the green circle marked A will turn the immersion controller on / off. The monitor sends a radio message to the power throttle which is near the immersion heater (or other heater) and regulates the amount of current flowing to the heater.
The power throttle is a white box with no identifiers on the outside. I have attached a photograph of the one controlling the immersion heater so you can see the positioning, and a photograph of the inside of the other as it's easier to get at. They are identical.
I hope that helps. I also hope you can open the photos in full size - not sure I've attached them correctly.

IMG_2044.JPG


IMG_2046.JPG
 

Attachments

  • IMG_20180808_0001.pdf
    2.9 MB · Views: 16
Hi - never fear, several of us have read through it all now :) . Doing my very simple logic on the problem - either there is an overvoltage and the unit correctly trips, or there is not an overvoltage and something else makes it trip but it (incorrectly) reports the fault as overvoltage. It might be interesting if you can create a trip by manually operating the immersion controller (?).
Thanks very much for your interest. It was Hansol who told me that it is overvoltage. The A10 has an LCD screen which shows an error message - E903. The User's Manual describes that as "Single fault event. Occurs on system connection standard single fault over. Contact the installer immediately."
I have not been able to provoke a trip manually. By observation I have been able to identify the most likely circumstances in which one will occur. I can turn the controller on and off manually - see my other reply today (to Marconi) with details of the controller. You can even turn the immersion heater on at full current manually - i.e. bypassing the automatic setting - that does not make it trip.
It appears only to trip when on automatic setting and the battery is less than approx 80% charged (but that may not be totally correct).
 
Thank you for your #4. The ESS displays a number of 4 digit fault codes beginning with E. See Section 9. Are any other codes other than E903 displayed please?

Also what ESS operation mode (see Section 8.3) is selected?

Also check that the current transformers are correctly placed, closed properly and plugged in.
 
Last edited:
First, did you ever have a period of trouble-free operation?

Second, could you provide a sketch of how the ESS, the Absolute energy controllers, the heater, immersion heater and your home wiring have been combined into a system, taking care to show where the current transformers are placed and to what (ie ESS or Absolute Controller) they are connected to.

It seems to me you may have two PV energy diverter/throttle systems working alongside each other and maybe not working coherently together. For example, the Abosolute Controllers have no planned interaction with the ESS Operation modes and vice versa. Thus there may be some unintended consequences.

It would be good if you could describe how it worked when you thought all was well.
 
The mains voltage monitoring you've had done appears within range. If it had been out of range, I'd expect to see E702 displayed and then restart after 1 minute, which is not what you've seen. So I don't think much of the advice you've had that there is supply overvoltage, two strikes I think.

IMG_1151.jpg
 
Thank you for your #4. The ESS displays a number of 4 digit fault codes beginning with E. See Section 9. Are any other codes other than E903 displayed please?

Also what ESS operation mode (see Section 8.3) is selected?

Also check that the current transformers are correctly placed, closed properly and plugged in.

Thanks for this. E903 is always the code when the system trips.
I'm afraid your question about which ESS operation mode is selected is too technical for me, and I don't understand what the manual has at section 8.3 on page 45.
I assume by 'the current transformers' you mean the white boxes in my photographs that Absolute Energy call the Power Throttles. They appear to be correctly wired, and the one in the airing cupboard was placed by Avonside. They both work perfectly well between tripping.
 
First, did you ever have a period of trouble-free operation?

Second, could you provide a sketch of how the ESS, the Absolute energy controllers, the heater, immersion heater and your home wiring have been combined into a system, taking care to show where the current transformers are placed and to what (ie ESS or Absolute Controller) they are connected to.

It seems to me you may have two PV energy diverter/throttle systems working alongside each other and maybe not working coherently together. For example, the Abosolute Controllers have no planned interaction with the ESS Operation modes and vice versa. Thus there may be some unintended consequences.

It would be good if you could describe how it worked when you thought all was well.

Yes, the system worked properly from installation (early 2016) until about
Thanks for this. E903 is always the code when the system trips.
I'm afraid your question about which ESS operation mode is selected is too technical for me, and I don't understand what the manual has at section 8.3, which appears to be Arrangement of Terms.
I assume by 'the current transformers' you mean the white boxes in my photographs that Absolute Energy call the Power Throttles. They appear to be correctly wired, and the one in the airing cupboard was placed by Avonside. They both work perfectly well between tripping.
Sorry - I got called away in the middle of replying and I think the system 'timed out', so this may be a bit disjointed. The fault developed in about May this year, so it worked fine for about 15 months.
I have drawn a diagram (attached) of how the system seems to me, but there are a lot of wires at the 'main switchboard', so I may not have got it quite right. However, what I know is right is that there is no direct connection between the Absolute Energy Master and the A1o. The Energy Master gets its information from clip-on sensors and sends 'instructions' to the power throttles by radio. The appliances get their power from the household wiring through the throttles. The two throttles are not working alongside each other - it is either one or the other. The one not in use is switched off at the wall and therefore cannot receive a signal from the control unit.
When it was working well, it was doing exactly what it does now, but not tripping. It was possible to leave it switched to Automatic all the time and whenever there was 'spare' electricity, instead of feeding it back into the grid, the control unit would divert it to whichever throttle was switched on. Now, whenever it trips, it doesn't just stop sending power to the throttle, it switches the whole system off, so it stops generating too.
 

Attachments

  • IMG_20180808_0002.pdf
    139.7 KB · Views: 13
Your immersion controller is a solarcache. They used to have technical guy called Trevor who was very helpful and maybe able to help you.
I have noticed that their website is down so I think you should try and get their contact details via midsummer

Thanks very much. I thought Solarcache had gone out of business too.
I'll see if I can make contact with Trevor (in the morning!)
 
Re: #9. Some more questions please.

1. Your diagram shows the Samsung A10 connected by a 'T' to the tails going to the consumer unit. Is this actually so? A picture would be helpful. I'd have expected the A10 to be connected to a circuit breaker in the consumer unit.

2. Where does the thin white wire shown on the left of the Absolute go to?

3. The current transformer are the devices which clip around the cables. Are they wired or wireless? Can you take some pictures?

4. Please confirm there is a current transformer clipped on the live or neutral leaving the A10. It must not be simply connected around both live and neutral. Again a picture would be helpful.

5. There should be another current transformer connected around one of the thick cables on the house side of the meter. A photo would be helpful.

6. Where is the A10 located? Is it getting too hot during the recent very warm weather?
 
Last edited:
The fault code is a 'significant' one which arises from a 'protection' fault which does not clear in time.

A possibility is the A10 is overheating because it has been inverting several kWs of PV electricity during long days of high intensity sunshine and is in a location which has a high ambient temperature and little ventilation. It will be interesting to see if during the next few days of cooler weather the system reverts back to normal operation. Maybe the forced air cooling by the 2 integral fans is less effective for some reason.

See 4.1.2 and 4.1.3 of reference which details a maximum ambient temperature of 40C and sufficient free space around the unit.

Can you hear the internal fans running? See 10.1 for fan maintenance and 10.2.4 for fan operation check. Are the grilles clear? How warm does the exhausted air feel? Perhaps stick a thermometer in the path of the air. It appears the fans have an operational life which may have been exceeded so they no longer run or run as effectively.
At 10.4.3 FAN 1 & FAN 2 it says:

In the All in One System, FAN1 and FAN2 provide air circulation to maintain and regulate the system temperature. The fans can be replaced when they reach the end of their operational life span or fail to work properly. If that is the case, the installer or the maintenance personnel will identify its cause of malfunction and will replace it. The replacement method may depend on the local maintenance conditions. The manufacturer's name and the model number of the fan are as follows: Minebia Manufacturing Company/DC FAN MOTOR/4710KL04W-B59-E00. For further details, please refer to the Maintenance Manual or contact SAMSUNG SDI Service. The contact address is described in Chapter 13.
 
Last edited:
Hi - thanks for confirming that manual operation of the immersion heater does not make the A10 trip. Along the lines of #20 can you confirm it never trips with the immersion controller switched off? Perhaps it is seeing an overload when trying to balance sending power to the battery or the grid and immersion controller winding the load up and down in accord with its own programme (?). As you say, if immersion is left on 100%, the system does not trip.
 
You have given me a clue. I checked the positioning of the current transformers (thanks for telling me what they're really called) and moved the export one. You say you would expect it to be on a negative cable, the diagram in the Energy Master installation guide shows it should be on the positive. I have moved it from the positive to the negative, and thought that had fixed the problem - but then it tripped. Even so, it has been more stable today than many other days. Could it be that simple??
I have to go out now, but will try and answer your other questions later.
 
Re #22. Please take a look at Figure 2 of:

https://midsummerwholesale.co.uk/pdfs/Solar-Cache-Installation-guide.pdf

You will see the positions of 2 current transformers. One (shown on the left of Fig 2 - measures export power) clips around any one of the two thick cables 'leaving' the meter to the consumer unit. The other one (shown on the right above the Consumer Unit - measures PV generation fed into the mains wiring) clips around the line(brown) or neutral (blue) of the output from the Samsung A10. Neither current transformer is clipped around the cables (positive and negative) between the solar panels and the A10.

Now, if you a current transformer clipped around one of the PV panel cables this is wrong. To move it to clip around the Samsung A10 line or neutral output will require an electrician to do it safely.

Please confirm you have an mcb in the CU for the PV.
 
Last edited:
Hi - thanks for confirming that manual operation of the immersion heater does not make the A10 trip. Along the lines of #20 can you confirm it never trips with the immersion controller switched off? Perhaps it is seeing an overload when trying to balance sending power to the battery or the grid and immersion controller winding the load up and down in accord with its own programme (?). As you say, if immersion is left on 100%, the system does not trip.

Yes, I can confirm that it only trips when the controller is set to automatic. You may be right about balancing sending power to the battery or elsewhere, but I'd have thought if that was the case it might trip when charging and, say, you turn on the kettle. Other things turning on or off round the house have never been a problem.
 
Re the kettle : If I've understood correctly the immersion controller (when on auto) is continuously fiddling the current to the immersion and the A10 may trip. And when immersion is manually on or off the A10 behaves normally. I think the kettle on or off is same as immersion manually on or off. No continuous load adjustment and no A10 tripping, if that makes any sense. It's only a theory, with no data to support ...
 
Re: #9. Some more questions please.

1. Your diagram shows the Samsung A10 connected by a 'T' to the tails going to the consumer unit. Is this actually so? A picture would be helpful. I'd have expected the A10 to be connected to a circuit breaker in the consumer unit.

2. Where does the thin white wire shown on the left of the Absolute go to?

3. The current transformer are the devices which clip around the cables. Are they wired or wireless? Can you take some pictures?

4. Please confirm there is a current transformer clipped on the live or neutral leaving the A10. It must not be simply connected around both live and neutral. Again a picture would be helpful.

5. There should be another current transformer connected around one of the thick cables on the house side of the meter. A photo would be helpful.

6. Where is the A10 located? Is it getting too hot during the recent very warm weather?

Sorry for the delay, also for my amateurish attempts at describing how it's all wired up. I have attached a photo - hope that helps. Sorry it's sideways.
To answer your questions in order:
1. There is a circuit breaker, but it's stand-alone, not in the main consumer unit. See photo.
2. The thin white wire is the antenna. There is one on each of the throttles and on the Energy Master control unit.
3. The current transformers are wired. You can see one in the photo. They connect to the Energy Master with phono plugs, hence the birds nest of thin black wires.
4. There is a current transformer clipped on the live wire leaving the A10. It is just out of sight to the left of the system consumer unit. The electrician who installed it looped the live wire out of the side of the unit and back in again to accommodate the current transformer.
5. See 3 above.
6. The A10 is on the floor directly below the photo. It has been getting warm there, but nowhere near 40 degrees. The fans appear to be working well and run at different speeds at different times.
 

Attachments

  • IMG_20180809_0002.pdf
    1.5 MB · Views: 15
Re the kettle : If I've understood correctly the immersion controller (when on auto) is continuously fiddling the current to the immersion and the A10 may trip. And when immersion is manually on or off the A10 behaves normally. I think the kettle on or off is same as immersion manually on or off. No continuous load adjustment and no A10 tripping, if that makes any sense. It's only a theory, with no data to support ...

Yes, that's right. However, when it's in the mood it can run perfectly well for hours at a time with the current fluctuating all over the place as clouds pass, the fridge goes on and off, someone uses the microwave etc etc. There seems to be no pattern to when it trips, only that it has to be set to automatic and (possibly) with the battery at a low percentage charge.
 
From the picture all seems connected correctly. I have exhausted the things I would have checked, albeit - clutching at straws - I'd run a calibration sequence on the immersion controllers see section 5 of

https://midsummerwholesale.co.uk/pdfs/Solar-Cache-Installation-guide.pdf

I suspect the battery or the cooling system - two sub-systems of the A10 which age with operational use.

Here is a website which might help you find a technician to attend your home:

Samsung SDI ESS Energy Solar Battery | Solar Guide - https://www.solarguide.co.uk/solar-batteries/samsung-sdi-ess-energy#/

When you discover what was the problem it would be nice if you cold report back.

:)
 
From the picture all seems connected correctly. I have exhausted the things I would have checked, albeit - clutching at straws - I'd run a calibration sequence on the immersion controllers see section 5 of

https://midsummerwholesale.co.uk/pdfs/Solar-Cache-Installation-guide.pdf

I suspect the battery or the cooling system - two sub-systems of the A10 which age with operational use.

Here is a website which might help you find a technician to attend your home:

Samsung SDI ESS Energy Solar Battery | Solar Guide - https://www.solarguide.co.uk/solar-batteries/samsung-sdi-ess-energy#/

When you discover what was the problem it would be nice if you cold report back.

:)

Just to keep in touch - Solar Guide are looking for an engineer who can come and look at my system and, I hope, diagnose the problem. So, thanks very much for their details. Fingers now crossed....
 

Reply to Problem with solar immersion controller and battery system. in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Greetings, everyone, After dedicating over a month to researching Solar PV systems, I'm nearly ready to make a decision. I owe my progress to...
Replies
1
Views
944
Hi, So I'm replacing a small old off grid with a new 7.5kw off grid, & being poor seek best value for my mppt, after long searches I find this...
Replies
1
Views
676
I currently have solar array and was going to purchase Shelly EM to monitor Grid in/out and solar production. So far so good. But I also plan in...
Replies
0
Views
1K
I currently have a 3Kwh solar PV system which was installed over 12 years ago and getting a very good FIT payment and I don't want to lose it! I'm...
Replies
0
Views
4K
I am installing a Victron Quattro in an island mode configuration (in the UK, the DNO is the NG). I will be adding a stand-by generator. My...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock