Discuss Problematic Ze........ in the UK Electrical Forum area at ElectriciansForums.net

All this is academic really if all circuits within the installation are 30ma RCD protected, it would have been more relevant in the past before such widespread use of RCDs was regulatory.
 
All this is academic really if all circuits within the installation are 30ma RCD protected, it would have been more relevant in the past before such widespread use of RCDs was regulatory.
It becomes academic if the protective device in the cut out takes longer than 5 seconds to disconnect due to a high ze/zs at the origin.
 
Yes but what of the thousands and thousands of TT systems with much higher Ze , they all have the same problem but much worse than your sub 1 ohm reading.
 
Yes but what of the thousands and thousands of TT systems with much higher Ze , they all have the same problem but much worse than your sub 1 ohm reading.
By that reasoning what's the point of the DNO stipulating max ze figures on tn-c-s and tn-s systems.
They are supplying an earth for the system and their figures should be upheld In my opinion
 
I'm not being argumentative Ian, just wondering if your perceived issue is really worth worrying about with the Ze that you have on this particular job. I just think a note stating DNO informed on your EIC would cover you fine.
 
The only way around the problem if the DNO cannot improve the Ze is to fit a main incoming RCD at the point of the incoming supply, that way the DNO fuses will take care of overcurrent and the RCD will take care of earth faults.
 
I'm not being argumentative Ian, just wondering if your perceived issue is really worth worrying about with the Ze that you have on this particular job. I just think a note stating DNO informed on your EIC would cover you fine.
Apologies dave I don't mean to seem to be arguing, I do see what your saying though about the tt system scenario.
I've never really thought about it in that light.
Food for thought mate.
 
With an all insulated head a TT system is not relevant, the DNO are not providing an earth so any fault requirement issues are not their problem.
With the OPs issue I am certain the fuse was reduced to 80A to allow an increased Ze.
 

Reply to Problematic Ze........ in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Evening everyone . I was changing a fuse board today . Everything tested out fine and good . Until I measured the Ze which is on a tnc-s system...
Replies
7
Views
880
On an EICR I found a 200 amp 3ph supply, TNS earthing (which looks original) and Ze of 19 ohms. No rods. No RCDs. L1 -> N was about 0.5 ohms...
Replies
11
Views
1K
Hi - just after thoughts on this please. I've been doing some testing on a 20 year old MCC. On the original EIC, Ze was reported as 0.04 R, PFC...
Replies
18
Views
2K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock