Discuss Protection for >3m tails in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

So for example, if you have a meter tail with approx. 0.5mm or so of shiny copper visible at meter end e.g. because the insulation has been stripped back a little too far, I'm hearing this should be coded C1, and needs an emergency call out of the DNO (since I'm not allowed to open the meter myself to correct it)?
 
Meters, henley blocks, and fuses are designed so that there is ample room to terminate and never leave any exposed copper. If there is any then it's a sloppy job and potentially dangerous.
It's up to you to assess whether it needs a call out or not. Exposed live parts would be worthy of a call out.

0.5mm might not let you get a finger onto it, but could a curious householder poking at the shiny stuff with a screwdriver to see what it is, get onto it ?
 
connector blocks are IP XXB by virtue of construction.
youd be hard pushed to justify a C1 or even C2 if it was not in an enclosure but otherwise undamaged and correctly fitted.

just thought i'd throw that little spanner in ;-)
 
connector blocks are IP XXB by virtue of construction.
youd be hard pushed to justify a C1 or even C2 if it was not in an enclosure but otherwise undamaged and correctly fitted.

just thought i'd throw that little spanner in ;-)

Ha ha, just for a change.
Ok I'll back up my choice by referring to the ESC EICR guidance which cites "terminations or connections without enclosure or barrier" as an example of a C1.
Also a connector block installed without enclosure would likely have exposed single insulation (C2) and inadequate cable restraint (C3).
In practice though I'd probably slap it inside a JB, and carry on. lol.
 

Reply to Protection for >3m tails in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi guys, could someone help with the following please? The scenario is: Domestic property supplied via three phase (with a 3P main DB, NO SPD)...
Replies
2
Views
501
Hi all, My question relates to the omission of overcurrent protection (specifically overload and fault protection) at the origin of an...
Replies
6
Views
2K
I don't "do" solar, but I've been asked to comment on an aspect of a new domestic solar installation by others. There is no overload or fault...
Replies
7
Views
1K
On a new build site how/ why are people getting away with installing meter tails over 3metres in length and behind dot and dabbed walls with no...
Replies
7
Views
2K
Was helping a friend out and changing their CU which had a date stamp from 1990. Good quality Merlin-Gerin unit and a nice job originally. They...
Replies
7
Views
815

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock