I'm familiar with current regulations for protection of meter tails over a certain (e.g. 3m) length, but what about a periodic inspection of a fairly old installation?

The installation in question has a Henley block, then an old isolator - looks to be perhaps 40+ years old, with no fuse - feeding a distribution board in a remote part of the house (in addition to an old fuse board close by the meter, also from the Henley block). The isolator looks in good condition otherwise. The distribution circuit is 10mm2 twin & earth, and maybe 15m or so long.

If this was acceptable practice at the time, does it need more than a C3 code now on an EICR for missing protection of long tails?
 
Last edited:
could be a potential danger if 10mm tails are protected only by the DNO fuse of 80A or 100A, in which case it's a code C2. if the tails show no sign of overheating, then you might give it a C3. your call, mate. personally, i'd quote for a 50A fused (or MCB) isolator. they're not a huge cost.
 
Thanks Tel. Actually I don't know the fuse size in the DNOs fuse carrier, and will only find out later, if I end up replacing the isolator (or the other fuse board). However, your post made me realize that because the tails are only 10mm T&E, probably it needs a C2 for that anyway with the mix of installation methods applicable. I'd still be interested in comments that suppose if the tails were larger, e.g. 16mm T&E clipped direct with an 80A DNO fuse, was that once OK and thus only need a C3?
 
suppose if the tails were larger, e.g. 16mm T&E clipped direct with an 80A DNO fuse, was that once OK and thus only need a C3?



AGREE.
 
Re: Protection for >3m tails

Due to the fuse board being remote there should be a local fuse adjacent the Henley Block anyway but due to size of cable I would C2 it and also add no RCD protection on cable as a C3

- - - Updated - - -

Due to the fuse board being remote there should be a local fuse adjacent the Henley Block anyway but due to size of cable I would C2 it and also add no RCD protection on cable as a C3
 
i thought the max length of tails was a dno , therefore an ESQCR , regulation.
you could argue it falls out of the remit of a inspection to bs7671.
if all other aspects of the tails are ok ( correct size , adequately supported / protected )
exactly which reg do you code against ?
mention it in the report , but without code.
 
i thought the max length of tails was a dno , therefore an ESQCR , regulation.
you could argue it falls out of the remit of a inspection to bs7671.
if all other aspects of the tails are ok ( correct size , adequately supported / protected )
exactly which reg do you code against ?
mention it in the report , but without code.


i agree up to a point, as regards the DNO and ESQCR comment, but you still have 10mm tails protected by an over sized fuse, which, IMO, warrants a code, even if only a C3,
 
Code 2 and a code 3 for no additional protection with it being T&E - presuming it's in a wall etc?
 
Thanks for the additional replies.

To sum up, if I’ve understood correctly, for tails over the length permitted by the DNO (typically 3m), suggested EICR code:


Cable not mechanically protected, e.g. T&E in walls
Cable is mechanically protected, e.g. SWA
Conductor size too small for DNO fuse rating, taking account of installation method(s)
C2 – needs fuse/MCB
C3 – recommend RCD
C2 – needs fuse/MCB
Conductor size OK for DNO fuse rating, taking account of installation method(s)
C3 – recommend RCD
No code – though does not meet ESQCR

This always assumes you know the actual DNO fuse size, e.g. a 100A carrier will often have a lower rated fuse fitted, which might not be easily checked.
 
not 100% happy with the C2's. if the cable is, say, 16mm on a 100A DNO fuse, and has been in situ for years without any signs of damage, i'd lean more towards a C3.
 
I'm inclined to agree, if 16mm2 cable CCC can be as high as 94A for reference method E, it is not that far short of the 100A. The trouble with having just three codes to choose from, with something marginal, I find it can be difficult to decide which code.

A different example I’ve come across a few times recently is small amounts of visible (exposed) live cable or terminals on the suppliers equipment, e.g. on the fuse carrier or meter tails, trying to decide if it should be a C1 rather than C2.
 
I'm inclined to agree, if 16mm2 cable CCC can be as high as 94A for reference method E, it is not that far short of the 100A. The trouble with having just three codes to choose from, with something marginal, I find it can be difficult to decide which code.

A different example I’ve come across a few times recently is small amounts of visible (exposed) live cable or terminals on the suppliers equipment, e.g. on the fuse carrier or meter tails, trying to decide if it should be a C1 rather than C2.

Accessible exposed live parts are always a C1, and in this case probably an emergency callout to the supplier/DNO.
 
Accessible exposed live parts are always a C1, and in this case probably an emergency callout to the supplier/DNO.

Yes, but I'm talking about quite small exposed parts, the question is whether they should be defined as accessible - comparing for example to an unenclosed choc block, a small one you can't touch the screws, make it large enough and perhaps you could.
 
Yes, but I'm talking about quite small exposed parts, the question is whether they should be defined as accessible - comparing for example to an unenclosed choc block, a small one you can't touch the screws, make it large enough and perhaps you could.

I would C1 compromised insulation on any live conductor, no matter how small, and a choc block of any size joining a live conductor not in an enclosure would get the same treatment.
 
Yes, but I'm talking about quite small exposed parts, the question is whether they should be defined as accessible - comparing for example to an unenclosed choc block, a small one you can't touch the screws, make it large enough and perhaps you could.

child with paper clip in sticky paw can access anything < IP4X. so code C1 for any exposed conductor or terminal , no matter how small the access is,
 

Reply to Protection for >3m tails in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi guys, could someone help with the following please? The scenario is: Domestic property supplied via three phase (with a 3P main DB, NO SPD)...
Replies
2
Views
501
Hi all, My question relates to the omission of overcurrent protection (specifically overload and fault protection) at the origin of an...
Replies
6
Views
2K
I don't "do" solar, but I've been asked to comment on an aspect of a new domestic solar installation by others. There is no overload or fault...
Replies
7
Views
1K
On a new build site how/ why are people getting away with installing meter tails over 3metres in length and behind dot and dabbed walls with no...
Replies
7
Views
2K
Was helping a friend out and changing their CU which had a date stamp from 1990. Good quality Merlin-Gerin unit and a nice job originally. They...
Replies
7
Views
815

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock