Code 2 and a code 3 for no additional protection with it being T&E - presuming it's in a wall etc?
never presume. look what happened to the titanic.
Discuss Protection for >3m tails in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Code 2 and a code 3 for no additional protection with it being T&E - presuming it's in a wall etc?
| Cable not mechanically protected, e.g. T&E in walls | Cable is mechanically protected, e.g. SWA |
Conductor size too small for DNO fuse rating, taking account of installation method(s) | C2 – needs fuse/MCB C3 – recommend RCD | C2 – needs fuse/MCB |
Conductor size OK for DNO fuse rating, taking account of installation method(s) | C3 – recommend RCD | No code – though does not meet ESQCR |
I'm inclined to agree, if 16mm2 cable CCC can be as high as 94A for reference method E, it is not that far short of the 100A. The trouble with having just three codes to choose from, with something marginal, I find it can be difficult to decide which code.
A different example I’ve come across a few times recently is small amounts of visible (exposed) live cable or terminals on the suppliers equipment, e.g. on the fuse carrier or meter tails, trying to decide if it should be a C1 rather than C2.
Accessible exposed live parts are always a C1, and in this case probably an emergency callout to the supplier/DNO.
Yes, but I'm talking about quite small exposed parts, the question is whether they should be defined as accessible - comparing for example to an unenclosed choc block, a small one you can't touch the screws, make it large enough and perhaps you could.
Yes, but I'm talking about quite small exposed parts, the question is whether they should be defined as accessible - comparing for example to an unenclosed choc block, a small one you can't touch the screws, make it large enough and perhaps you could.