Discuss Put a ring circuit in a garage. in the DIY Electrical Advice area at ElectriciansForums.net

setinomad

DIY
Reaction score
0
Hi there. I'm a DIYer. Just bought a house with a double garage that has just one socket in it; and it seems to be just a single spur direct from the CU. I want to put in more power outlets; and was wondering whether it's permissible to remove the existing socket, put in a 32a fuse/breaker, and then run a small ring circuit within the garage with a handful of sockets on it.
 
If it’s only a handful of sockets, and not a high total load, it could be a dedicated 16A radial, wired in 2.5mm

Edit: As you say, if its a SPUR you can only have one socket. You would need a spare way in the consumer unit for either a radial or a new ring.
 
Last edited:

Reply to Put a ring circuit in a garage. in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi, if getting back to the CU is not an option, instead of spurring off a socket via a Sfs putting the rating down to 13a. Could you spur off the...
Replies
43
Views
2K
I may have posted this before but not sure if it made it in. I want to install an EV Charger in my garage. The panel is two stories up and the...
Replies
0
Views
485
Hi everyone, I've got a garage with a circuit that looks like this: I believe it's a radial circuit coming out of the MCB with a current...
Replies
8
Views
2K
Hi, just helping someone out and apologies for the long winded post. Would like install a couple of weatherproof double sockets on the patio. 1...
Replies
3
Views
736
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock