Discuss Pyro Cable Tripping RCD in the UK Electrical Forum area at ElectriciansForums.net

S

sl1210

Went to a job in a church hall today where one of the power circuits was tripping the rcd. There seems to be 4 bad legs of pyro in the circuit, as I get a dead short in my IR tests between line/neutral, line/earth.

Is it common for pyro cable to do this after a certain time, or could a fault have caused this?

I have disconnected all the faulty legs and managed to keep the rcd on with only one socket working. I'm going to have to re-link the damaged pyro with new cable.

Was wandering if I could use 2.5mm FP cable clipped direct, or whether because its a church hall i would need to run it in plastic conduit???

Cheers
 
you can use whatever the church authorities will accept, as long as it also complies with regs.
 
We once experimented with pyro and a BIG hammer. The cable was almost completly flat in CSA before the conductors shorted out.

There must be some extreme damage ( possibly cuts ) somewhere...

Continuity measurements shoud indicate roughly how far away the short circuits are from the CU ( thats length of cable NOT actual distance as the cable could follow a long route to get a short distance.
 
not that i can see mate.

basically what i did, was create a temporary plug top on a lead with a connector block. i then plugged this into a working socket via an extension lead, to see what didn't trip.like i said 4 pyro cables tripped the rcd when connected. really strange, cos i know that pyro is normally made for life right???

i need to relink 4 sockets. just not sure whether to use fp2000 clipped direct or plastic conduit with metal surface boxes???
 
you havn`t got any connected loads have you that may be causin this?....
or has the pyro been left unterminated...and has been exposed to damp?.....if so you can drive out the damp with a blowtorch....
 
nope no loads. and i removed all the faces and was testing open ends. they are internal exterior walls they run along. you think it could be damp????
 
it's quite possibly damp. stick your IR test on the cable/s , use 1000V if your tester will do it, and leave it connected for a minute. if the reading improves, then it's probably damp.
 
my megger only goes up to 450v.

nope trips straight away. its so strange because there are three runs of pyro on the left of the hall doing it, and one run on the right of the hall.

i think i will just replace it anyway because, i'm guessing theres a chance it will get damp and trip again anyways even if i did dry it. now that you have said that i'm always certain that it is a damp issue. but would damp cause a dead short???
 
good call. a continuity test might be advantageous.
 
just replace the micc with new silicone impregnated micc
old micc is notorious for ingress of moisture at the pots
if its bare micc you can gently remove the seals and compound then unscrew the pots and drive the moisture out with a blowlamp
but u need to be about 60(me) to know what your doing
sticking some other cable inbetween is a crap bodge up imo
 
I find it strange that four lengths of Pyro have gone down at the same time and can't help but feel the OP's lack of any useful experience with Pyro is not helping in identifying the problem or it's cause

It would be interesting to have sight of the last PIR / EICR to check the IR values of the circuit in question when it was last tested
 

Reply to Pyro Cable Tripping RCD in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

So was on a call out today and cooker circuit kept tripping the RCD. Disconnected at the board and at the cooker switch and IR’d the cable and...
Replies
9
Views
400
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
807
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
342
I have just checked a double outlet and it trips at 18ma. It was supposed to be faulty. Washing machine had a bad heater which got replaced but...
Replies
10
Views
580
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock