Discuss r1+r2 testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

J

james king

hi all just reading up on continuity testing (r1+r2 test) say i have a ring main of 40m long serving 10 sockets..

the reading i have got is say 0.35ohms

but on 1 socket i have a higher reading of 0.46ohms

now i have learnt at collage this may be caused due to a loose connection

could this also be due to a spur?

are spur readings usally higher
 
High R1&R2 readings can result from loose connections, however the r1, rn & r2 tests would normally be done prior, and in doing this, the loose connections will become apparent. The most common example for high R1&R2 readings used in syllabus is a spur, or 'ring within a ring' arrangement. I am surprised that loose connections was used as an example.
 
The R1R2 reading of a ring with a spur will be the R1R2 of the ring ,plus the R1R2 of the cable between the point of connection to the ring and the socket served by the spur.
 
please can u expand on ring within a ring?

a ring within a ring is pretty much what it says where a second ring has been added to the original, in itself this is not a problem unless the ring gets broken somewhere then you will have a ring with a radial attached when testing you would find all sockets on the ring read as they should but the radial readings will increase as you move outward
 
Can u give me some examples of what reading u would expect if you were to plug in ur tester to a spur please sorry about caps

Say the R1+R2 reading for the socket you're testing at is 0.35 Ohms and a spur has been taken from this point, say 10 metres of 2.5/1.5 pvc/pvc cable then your R1+R2 at the spur will be approximately 0.45 Ohms (allowing 0.10 Ohms for the spurred length of cable).

When this value (assuming it is the highest on the circuit) is added to the Ze or Zdb, you have the Zs for the final circuit.
 

Reply to r1+r2 testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi All, Had a weird one this morning during an EICR. Testing a ring final circuit in a 2 bed flat… kitchen was on a separate ring. With only the...
Replies
7
Views
1K
Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
Replies
7
Views
867
Hi Can anyone clear up or explain in a bit more detail what could potentially be causing the results I have. I have just tested a 32a ring main...
Replies
7
Views
1K
I have been asked to look at this report as the customer has been given (in their words) 'A very high quote plus VAT'. It doesn't look well...
Replies
5
Views
644
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock