Now chaps,

Will a radial circuit on a 20amp rcbo be enough to power a washing machine, dishwasher, dryer and fridge freezer?

At the moment the radial has a 2 gang to power 2 appliances and a 1 gang to power fridge freezer, possibility of spuring of this circuit to power an extra appliance?


Cheers.
 
bear in mind diversity.
1587632857482.png
not all appliances will be drawing power at the same time .
 
I wouldn’t.

Theoretically yes it would work, but good design would put a kitchen circuit as a separate ring from the rest of the house Due to the high loads On appliances.

3 of the highest loads on the property on a 2.5mm, I would say is boardering on not good design.

A 4mm radial I would be happy with.

edit: one other point I would make is I never put 2 high load appliances on one 13A double socket. From experience of many call outs they tend to burn out Over time.
 
I wouldn’t.

Theoretically yes it would work, but good design would put a kitchen circuit as a separate ring from the rest of the house Due to the high loads On appliances.

3 of the highest loads on the property on a 2.5mm, I would say is boardering on not good design.

A 4mm radial I would be happy with.
butOP might have a separate ring for the rest of the kitchen sockets and wanting the radial just for these appliances?????
 
butOP might have a separate ring for the rest of the kitchen sockets and wanting the radial just for these appliances?????
Those 3 appliances alone pretty much are the vast majority of a kitchens load on a normal kitchen ring. Putting them on a radial is lowering the current carrying capacity considerably.

Having a ring for the rest of the kitchen wont take that much load away.

i accept design and calc wise it is acceptable, but i would like to give it that bit more current carrying capacity.
 
The radial in question is in the utility, the kitchen has 2 separate radials with a total of 3 double sockets.
[automerge]1587634320[/automerge]
I'm hoping to start my extension in the next couple of years so it will all be complete new design and re wire, not that it makes any difference haha
 
Putting a fridge-freezer on a circuit with a higher than usual chance of tripping is not good, you go out for the day with something running and come back to find half your food is defrosting!

If rewiring/replacing then you could put in 4mm cable for a bigger radial, or if it is feasible add another 2.5mm run to the far end and turn it in to a ring, putting that on 32A breaker.
 
Never thought of that, what if I extended the radial to a fused spur then the extra appliance to the fused spur, if overloaded would that pop the fused spur or would it still trip the rcbo? This is temporary until the extension goes ahead.
 
Just wondering out loud about "if regs. permit, MCB" for higher reliability (less nuisance tripping) for the power feed.

Obvious issues are RCD protection for buried cables less then 50mm from wall surface, so that can be mitigated with Flexishield cable more definitely than allowing others to install stuff.

What is the position on a 13A socket without RCD protection, is it OK if labelled and intended for use with a fixed appliance such as a fridge-freezer? Using a FCU would seem a lot of future trouble for the home owner for such an item.
[automerge]1587636268[/automerge]
Never thought of that, what if I extended the radial to a fused spur then the extra appliance to the fused spur, if overloaded would that pop the fused spur or would it still trip the rcbo? This is temporary until the extension goes ahead.
Generally no, it won't help. Circuit breakers (MCB and RCBO) usually trip faster than fuses blow. Also there it is the concern of other things tripping (e.g. water leak for RCD).
 
Last edited:
I also put the beer fermentation equipment on a non-RCD circuit. can't have the beer spoiling, can we?
I see you can easily buy a still these days... very tempting in these times of lockdown and reduced workload to have a play with that ! And it'll use up the potato peelings !
 
if overloaded would that pop the fused spur

The fact that you are thinking about what will happen when the circuit is overloaded means the design is inadequate, never mind the F/F going off unexpectedly. As mentioned, appliances that use water have a higher than average probability of causing a leakage trip and automatic machines run unattended when no-one would be aware of the trip, so an ideal setup would not put them on the same circuit as the refrigeration.

The dryer is more or less a constant 2kW load, so if the washing machine and dishwasher heaters come on at once, the circuit will be overloaded at up to 30A. Although you can allow diversity when a large number of items are in use, two appliances that might be started on their programmes at the same time and heat water from cold for maybe 20 minutes at a time before their thermostats take effect, do not in my book constitute a diverse load. We often start multiple machines at once at home.

So no, I would not do this. A 32A radial could take more load in addition, as then you can legitimately start to apply diversity.
 
Ideally yes, but replacing current radial with new 4mm will be very difficult, with tiled walls and floor lol
20 amp it is then, advise the customer against running all appliances at the same time.
 
Ideally yes, but replacing current radial with new 4mm will be very difficult, with tiled walls and floor lol
Is there any other way to add another cable? What about going outside route for part of it using SWA?

When they talk about "replacing" you do not have to remove the old one - it could be reused as a dedicated feed for the F/F (assuming not on the same RCD at the CU).
 
Is there any other way to add another cable? What about going outside route for part of it using SWA?

When they talk about "replacing" you do not have to remove the old one - it could be reused as a dedicated feed for the F/F (assuming not on the same RCD at the CU).

No space on cu to add mcb or rcbo
 
No space on cu to add mcb or rcbo
Could you run another cable though?

You could temporarily retire the 2.5mm but keep it for later re-use (assuming you ever get a new CU with more space), and at least go for a 4mm feed to allow a 32A radial there. That won't deal with the RCD trip risk issue, but it would overcome the marginal total current situation.

Going one step further, if you can feed something like SWA (or Flexishield) that does not require RCD protection then you could feed it off a MCB at the CU and then fit a "garage" style small CU in that area with a couple of RCBO to give some fault tolerance.

Yes, it is hard to get selectivity on over-current with a MCB feeding another MCB (the overcurrent part of an RCBO) but depending on the cable and system Ze value you might get away with quite a high trip for the feed (as it only has to provide short-circuit protection with a 5s clearance time) and a couple of smaller RCBO that if they trip per-appliance fault it is not really any more of a deal than the plug's fuse popping.
 

Reply to radial circuit to power washing machine, dryer and dishwasher in the Electrical Appliances Forum area at ElectriciansForums.net

Similar Threads

Currently planning a new rewire for my kitchen and want to get things right first time when it comes to appliances consumptions and circuits...
Replies
0
Views
1K
Hi all. So I'm designing my new kitchen and trying to plan where things will go. I currently have a 6 switch panel for the appliances (hob...
Replies
18
Views
1K
Hi everyone. The title should sound crazy enough, but it's what happening in my 72-years old home we've purchased 2 years ago. I found the crazy...
Replies
1
Views
517
HI All, I am building a new house (self build) and have my part P so am running the cabling. My reading of the regs says that any appliance of...
Replies
18
Views
4K
Hello everyone, I'd like to seek your input on a matter. I'm in the process of designing the electrical connections for the following kitchen...
Replies
38
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top