Guys needvadvice please
I was asked to carry out an annual inspction of a DB recently
There are 12 in number radial circuits suppling sockets wired in 4mm singles protected by 32A mcb the cables are enclosed in metal trunking and supply 13a socket outlets , are the mcbs now overated as the cables are now rated at 28A maximum due to the wiring method and should I also be fitting rcbos as the installationis is classed as unsupervised
It is a large office and the socets are for IT equipment my intention are to downrate the mcb or rcbo to 25A if they are available.
Thanks Dimspark
 
Guys needvadvice please
I was asked to carry out an annual inspction of a DB recently
There are 12 in number radial circuits suppling sockets wired in 4mm singles protected by 32A mcb the cables are enclosed in metal trunking and supply 13a socket outlets , are the mcbs now overated as the cables are now rated at 28A maximum due to the wiring method and should I also be fitting rcbos as the installationis is classed as unsupervised
It is a large office and the socets are for IT equipment my intention are to downrate the mcb or rcbo to 25A if they are available.
Thanks Dimspark
Check table 4D1A.
Ref method B.
2 cables, single phase 😀
 
Check table 4D1A.
Ref method B.
2 cables, single phase 😀
Thanks
Dimspark by name need to get new glasses had to ask the question as on other sites a subby is swapping out 32A for 25A breakers and are also 4mm single phase and I was asked to do this particular board because it had been missed and no report has been produced I do feel like a Dimspark now
Thanks for the reply HappyHippyDad
Thanks Pretty Mouth
Check table 4D1A.
Ref method B.
2 cables, single phase 😀
 

Reply to Radial Circuits Wired in 4mm and 32A MCB in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

i have just started my course as a trainee electrician...some advice on the following will be appreciated: I have a spare 16 and 32A MCB (RCD...
Replies
5
Views
325
Hi guys, We’ve had a new CNC Machine from China arrive this week. It came with a monitor and a tower to run the software. The monitor and tower...
Replies
7
Views
868
Ok i may get slated for this one but here goes; A bit of background info first. Its been a while since ive looked at my iee regs, and ive not...
Replies
12
Views
2K
Came into work today with a fairly urgent requirement to install an instant hot water handwash unit in a small commercial kitchenette/servery -...
Replies
19
Views
2K
Hello Electrical world. Looking for thoughts and opinions. Currently planning out my kitchen re-wire for new kitchen. I was originally...
Replies
13
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock