Discuss radial from ring main in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Just 'cos we've never done it, nor considered doing it, doesn't mean it's not right! Rather than blindly reading and (mis)interpreting the regs. it's good to think about these things sometimes.

It's clear that this is not covered specifically in the regs. One the plus side, there are no current carrying capacity problems using 4mm. On the down side there's wonky ring syndrome. Now correct me if I am wrong, but I could fit 4 fused spurs off 4 adjacent sockets quite happily and 'correctly' and unbalance me ring.

must be an awful feeling to have one's ring unbalanced.LOL> seiously. valid point there. it's only recently that the trade has been questioning the use of ring finals. rings have been used for socket circuits for years, just because that's the way we've always done it. ( well, since the war when copper was in short supply).it is good to question why things are done in a certain way. it's called progress.
 
Next week we shall discuss a 4mm ringmain on a 40a mcb. oh hold on hav,nt seen that in the regs book.

Table 6E1 OSG. 4mm, ref method B = 30a therefore on a ring main final it can carry 60a (on a balanced ring). But as we all know the maximum mcb/rcd can only be 40a in a domestic installation so this is fine. What can we talk about next week?

Ps, regards to regs for ring balance look at reg 433.4, 433.4.1 and 433.4.2
 
Last edited:
So, to all that have posted that it is fine to spur from a 32A, 2.5mm T&E ring final to any number of socket outlets without an FCU beforehand, can you tell me how it is we arrive at the scenario whereby it is fine to protect a cable with a CCC less than that of the associated OCPD, and the fundemental principals that allow us to do this???
 
You can't. The cu mcb/rcbo must not be rated higher than the smallest csa of that circuit. In this case the OP must take this into consideration. That way the demand from all appliances on the 4mm can not be higher than the supplying 2.5mm cable if its the first on the ring and therefore not overloading any one section of that ring.
 
Last edited:
You can't. The cu mcb/rcbo must not be rated higher than the smallest csa of that circuit. In this case the OP must take this into consideration. That way the demand from any ---- in the 4mm can not be higher than the supplying 2.5mm.


So why then do we have a 2.5mm T&E protected by a 32A MCB???
 
Worse case scenario, 2.5mm in three core enclosed in conduit in an insulated wall = 17.5a. So on a ring it would double to 35a and having a lower fuse to 32a to protect the cable. To spur off that ring without overloading a single section wild need investigation to the load on the ring before spurring off it. If your spurring off the first socket you will put the majority if the load on a single part of 2.5 on the ring and that's not good. (balanced ring).
 
Can someone please tell me why Appendix 15 suggests a 4mm radial circuit should be protected by a 32A Breaker when the only installation method that this would suit is clipped direct.

Sorry to sidetrack the thread but i have always wandered.
 
Can someone please tell me why Appendix 15 suggests a 4mm radial circuit should be protected by a 32A Breaker when the only installation method that this would suit is clipped direct.

Sorry to sidetrack the thread but i have always wandered.

A 2.5mm ring = a csa if 5mm so any cable less than the ring can be protected by the same mcb. If it was a 2.5mm radial you can still increase the csa if the spur cable long as the main mcb is protecting the 2.5mm. Hence the reason for a fcu to protect the spurred cable and the flc for that spur.
 
Ok my understanding don't shoot me !!! The idea of balancing a ring is crap the ring in its nature if installed correct is balance through each leg being as near as same length. If the first socket in that ring is used most of the current will go down the shortest leg and the rest the long way around correct!!! You can only spur once of a ring if no switched fused spur is used reason being you could connect 4x double socket on it and carry 32a on a 2.5 or 4mm but it would overload the shortest part of the ring it connects too. The reason we fuse it can not carry more than 13a due to the fuse therefore no different to pluging some thing in that pulls 13a!!! so the fact is 1x socket if spuring without fuse with fused spur as many as you want it will still only pull 13a. I hope that makes sense? You could do loads of stuff if you just look at one part of the regs it overlaps! The regs are for guidance they just prove or disprove you are breaking the law electricity at works !!:rolleyes:
 
So, to all that have posted that it is fine to spur from a 32A, 2.5mm T&E ring final to any number of socket outlets without an FCU beforehand, can you tell me how it is we arrive at the scenario whereby it is fine to protect a cable with a CCC less than that of the associated OCPD, and the fundemental principals that allow us to do this???

lenny you.ve missunderstood.4mm cable has a ccc higher than the ocpd of a 2.5mm ring main.read the thread from the start,and calm down dear
 
lenny you.ve missunderstood.4mm cable has a ccc higher than the ocpd of a 2.5mm ring main.read the thread from the start,and calm down dear

I have read the thread from the beginning thanks

My point is that you clearly dont understand the fundemental principals of a 2.5mm T&E ring final circuit protected by a 32A OCPD, and the effect 'spurring' off to multiple socket outlets without an FCU beforehand will have on that circuit, frankly that shocks me a little.
 
I have read the thread from the beginning thanks

My point is that you clearly dont understand the fundemental principals of a 2.5mm T&E ring final circuit protected by a 32A OCPD, and the effect 'spurring' off to multiple socket outlets without an FCU beforehand will have on that circuit, frankly that shocks me a little.

even if the spurs are from near to distboard a percentage of current will flow long way round. As 2.5 carrys 80 plus percent of total possible load {32a} i dont think your objections are as well founded as you think they are
 
hi there, would like your views on this.. Jb off a ring main and run two or three socket,s on a 4mm radial. I myself don,t mind it. no current capacity issues.and no zs problem,s if rcd protected.Any thoughts.

You asked for peoples thoughts, you got them!!!

Seems to me you will do what you want to do anyway, so carry on.
 
Hi everyone,
how about this one then.

outside socket is currently part of a small 2 bed flat ring.

the outside socket has been discarded and an adaptable box has been placed there. From there 4mm swa approx 6 metres into a small summer house feeding 4 sockets and 2 4ft flourescents.

the 4mm swa is made of into a small c/unit and all wiring is in plastic conduit. the small c/unit has a 63a double pole isolator ( no rcd protection as the flat ring that the swa is spured off from is protected by rcd already.

I am carrying out an inspection on this, so would you say this is ok, or not to regs etc.

Thanks for ready and any advise etc would be helpful,
Sav
 
even if the spurs are from near to distboard a percentage of current will flow long way round. As 2.5 carrys 80 plus percent of total possible load {32a} i dont think your objections are as well founded as you think they are

Have you actually read 433.1.5 and thought about the path of least resistance?
 
No thats not ok !!! Only if you take the adaptable box out and put a switched fused spur IP Rated with a 13a fuse in. The main switch is not rated to the 4mm and it could carry more than 13a !!!!
 
No thats not ok !!! Only if you take the adaptable box out and put a switched fused spur IP Rated with a 13a fuse in. The main switch is not rated to the 4mm and it could carry more than 13a !!!!

Why not leave the adaptable box where it is !!!!!!! Its big enough to fit a 13a SFCU inside it and its IP65 rated !!!! . Also why the !!!!!, i only asked thats all,
Thanks
Sav
 

Reply to radial from ring main in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Essentially I have a "normal" socket in a ring mains, i.e. one 2.5mm T&E going in and one 2.5mm T&E going out. I am looking to simply add two more...
Replies
2
Views
292
HI All, I am building a new house (self build) and have my part P so am running the cabling. My reading of the regs says that any appliance of...
Replies
18
Views
4K
Hello, Last year I had some electrical work completed in my house (New CU, SWA for garage, downlights) I informed the electrician that I will be...
Replies
8
Views
2K
Hi all, I'm planning to remove a stud wall seperating my dining room and kitchen. On the dining room side of the stud wall, there is a double...
Replies
1
Views
1K
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
275

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock