Discuss radial from ring main in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Sorry no offense intended I just always do it lol Sorry. I dont understand why this is still going really its the same as an extention lead you can plug what the hell you like in it as long as it does not go over 13a. The reason is not because of the ring being in balanced but more to protect the cable in the spur as the balance is maintain as it enters the ring in the same place and is no different to pluging in something that pulls 10a hello in balance!
if you spur off the spur without a switched fused spur the only limit is the mcb 32a. The idea is sound without problems no way the spur can take more than 13a s. Am I making sense lol
 
This topic is very bitchy, I think everyone knows how to do it properly (probably an overstatement there) but I'd imagine most people that take the time to read through a forum like this would want to do it properly.

If your going to take a 4mm up just take two 2.5mm's up, split the ring and then it's done in a proper and recognised way. If I saw that 4mm method done at a job I'd instantly think DIY.

It's pointless getting so ---- about doing it a different way for such a nothing job. And I don't mean that in an offensive way. I'm more talking about peeps that start studying the BRB for reasons why or why not to do it. Let it go people there's more to life than ********.

Hope this helps :)


Sent from my iPhone using Tapatalk
 
I've just done a search on Google for:- balanced ring main, to find out once and for all what the intelligence of the world wide web had to offer. Guess what came top if the list? My rant on this thread post 42. Just goes to show that you can't believe everything on the internet.;););)
 
On the issue of the unbalanced ring. Assume 3 X 3KW fires connected on unfused spur (I have seen it done in one room in order to dry plaster/paint) assume that the spur is connected 1/5 of the way around the ring and there is no other load on the ring.

9KW = 39A which will not trip a 32A MCB in a hurry. 1/5 of 39A will go the long way around (7.8A) and 4/5 will go the short way (31.2A) this is in excess of the 23 A for 2.5T&E installed to method B.

I will leave it to others to do the calcs on how long before the 2.5 T&E gets a bit hot and to access whether the scenario is reasonable. A load of 28.75A would not overload the short leg of the ring in the above scenario (23A = 4/5 of 28.75)
 
Jaresquire,
The load on the short leg of the extended would be the same as my example, an unbalanced overloaded segment of the ring. Which is what I suspect your question implied.

A good reason not to have rings, the users do not know/care about unbalanced loads. After all it has been properly installed, how can they overload it without a fuse/breaker tripping, they will ask when their house has burnt down. Having said that how many fires have been caused by an overloaded ring never mind an overloaded segment? Stats appear to show very few if any.

As someone said before why all this fuss about something we would not install? But I am one of the guilty parties by continuing to post:-(
 
Reasons you shouldn't:
  1. It is prohibited by 434.2.1 - "The part of the conductor between the point of reduction of cross-sectional area or other change and the position of the protective device shall not exceed 3m in length..."
  2. It is prohibited by Appendix 15 - "An unfused spur should feed one single or one twin socket-outlet only..."
  3. It is unprofessional - ingenious little 'solutions' like this are the hallmark of the DIYer.
  4. It's easy enough to do it properly, ie in accordance with the regs.
  5. It creates unnecessary confusion for someone unfamiliar with the installation - the spur appears to be an A2 radial but leaves the consumer unit as an A1 ring.This could even be dangerous when it comes to isolation.
Reasons you should:

Apparently it's easier to take 1 cable up to the loft, although it's easier to get 2x2.5mm cables into the terminals than 2x4mm.

... And that still doesn't explain why you can't fuse it down, like an extension lead.
 
Last edited by a moderator:
Reasons you shouldn't:
  1. It is prohibited by 434.2.1 - "The part of the conductor between the point of reduction of cross-sectional area or other change and the position of the protective device shall not exceed 3m in length..."
  2. It is prohibited by Appendix 15 - "An unfused spur should feed one single or one twin socket-outlet only..."
  3. It is unprofessional - ingenious little 'solutions' like this are the hallmark of the DIYer.
  4. It's easy enough to do it properly, ie in accordance with the regs.
  5. It creates unnecessary confusion for someone unfamiliar with the installation - the spur appears to be an A2 radial but leaves the consumer unit as an A1 ring.This could even be dangerous when it comes to isolation.
Reasons you should:

Apparently it's easier to take 1 cable up to the loft, although it's easier to get 2x2.5mm cables into the terminals than 2x4mm.

... And that still doesn't explain why you can't fuse it down, like an extension lead.


The end........
 
So went to help out a new company as a subby today possibly for more too as electrician they had onboard was keen on drink ;-) lots of it stashed on site etc..
They have a 1st yr apprentice left there trying to basically learn to fit new kitchen wiring and bathrooms with no knowledge at all basically and while elderly people are still living in the flats high rise.

I start looking to fit new socket faces and general 2nd fix and test today and find back boxes all steaming etc.. and the tiler has tiled at 55 degree angles to the boxes that were already on the lash ! then I get to asking him- apprentice why they have run spurs off spurs off spurs from original ring all in 4mm twin no less at a guess to carry the current as opposed to 2.5 and extending the ring final, and they have in a few flats looped 4mm twins in and out and picked up DP switches to isolate sockets in alcoves etc.. for washing machines and the like then added as I say spur after spur essentially making one point of the entire flat ring circuit into a radial.

Then at one end they have fed 4mm into a single box to feed a switch for an extract fan up above and come straight off in 1.0mm twin ! I said why not into a SFCU to enable fusing it down at least but he said two sparks said it was all good ?? well he said one said he wouldn't do it like that but it was ok !

Next flat even better same issue mainly spur off ring and then as a radial to 6 plus sockets or DP switches and on to sockets after, then I ask where is feed from ring in ? Young lad says oh it's there other side of kitchen ! So I look and no they have a cupboard with a big slack heap of 4mm bundled in there, then he says oh yeah there's a feed the other side to opposite work top and units too, no linking cables up and over etc.. just the single 4mm one side spurred off the ring and other side of kitchen everything is linked together and waiting to be fed separately from the 4mm bundled in a hall cupboard ! So by now I'm thinking someone has a big hat and horse outside, and so in for a penny I ask him where the previous spark had said he was taking the 4mm ? and he says just in the back of that single socket in the hallway to feed the kitchen as a spur !!

Where do these people come from and how can they sleep at night !
Am I just being picky or is it utter shi*e ??
 
hi there, would like your views on this.. Jb off a ring main and run two or three socket,s on a 4mm radial. I myself don,t mind it. no current capacity issues.and no zs problem,s if rcd protected.Any thoughts.
I would suggest you read, inwardly digest Appendix 15 of the BS 7671, which give you all the details of Ring final circuits and Radial final circuits, what you are suggesting smacks of " you don't know what you are doing" sorry for being blunt but this is basic stuff for even a DI
 

Reply to radial from ring main in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Essentially I have a "normal" socket in a ring mains, i.e. one 2.5mm T&E going in and one 2.5mm T&E going out. I am looking to simply add two more...
Replies
2
Views
292
HI All, I am building a new house (self build) and have my part P so am running the cabling. My reading of the regs says that any appliance of...
Replies
18
Views
4K
Hello, Last year I had some electrical work completed in my house (New CU, SWA for garage, downlights) I informed the electrician that I will be...
Replies
8
Views
2K
Hi all, I'm planning to remove a stud wall seperating my dining room and kitchen. On the dining room side of the stud wall, there is a double...
Replies
1
Views
1K
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
275

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock