Discuss RCBO for this CU? in the UK Electrical Forum area at ElectriciansForums.net

O

Octopus

Being lazy (yes I know) but I'm so, so busy at the mo!

Need to find a 6A RCBO to fit this board, can anyone point me in the right direction?

Crabtree CU.jpg

Thanks......
 
crabtree starbreaker. nothing else will fit. any crabtree stockist should have them. they're not obsolete.
 
Are those the breakers that have unshrouded screw terminals low down in the body and slightly off centre, same as the old Wylex NB? If so, not sure you'd get a 'standard' modern MCB to fit. Not sure they ever made RCBO's to fit either, but stand to be corrected. The couple of times I've taken one of those MCBs to the wholesaler I've come away with modern far eastern 60898 equivalents.
 
there are 2 types of breaker used on the starbreaker range,the early ones are almost identical to the wylex with the screw to attach to busbar.Later starbreakers used a tongue on the back that went into the busbar (pushfit) if its that type and you get stuck the big orange shed does them.
 
This board is a Crabtree SB6000 Starbreaker with the standard copper finger busbar and screw fixed protective devices (pre plug-in Starbreaker). The only RCBOs available for these early boards are 2 modules wide, looking like an MCB with an RCD stuck on the side. The MCBs and RCBOs for SB6000 boards were available in Types 1 and 2 only.
 
This board is a Crabtree SB6000 Starbreaker with the standard copper finger busbar and screw fixed protective devices (pre plug-in Starbreaker). The only RCBOs available for these early boards are 2 modules wide, looking like an MCB with an RCD stuck on the side. The MCBs and RCBOs for SB6000 boards were available in Types 1 and 2 only.

So if I get one it won't fit anyway.

Thanks for the info!
 

Reply to RCBO for this CU? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

So here is the thing Rhere is an old MEMSHIELD TPN+E Board that is pretty mich obsolete. The only place that sells their breakers would be Ebay...
Replies
5
Views
862
I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
764
Hi all, Wondering if you could offer some advice please. I carried out a small outdoor lighting project today at a commercial property. 4 lights...
Replies
5
Views
952
Hi, I recently had an EICR done at my property which unfortunately was unsatisfactory. So the electrican advised a new fuseboard from BG General...
Replies
90
Views
3K
Hi all, I needed to replace an MCB for an electric shower with a different rating, it's an older Loadstar consumer unit, and crabtree told me word...
Replies
1
Views
740

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock