Discuss RCBO tripping advice. in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
39
Evening All...I've not posted in a while which is a good thing as I can now work most things out myself!!

Just a bit of help needed with this one though!!

I have two consumer units, both have a mixture of MCB's and RCBO's on one of the consumer units the RCBO's are tripping randomly (The customer is adamant that it's since the smart meter was installed but probably coincidence),

I have done an IR test on the circuits with the RCBO's and they all pass. I didn't have time to test all the other circuits today but will do next time.

My question really is..would a N to E fault on the non-RCD circuits cause the RCBO to trip?

I'm just wanting a bit of info to go back with tomorrow as they customers are OAP's and they have had sparks look at it the past and not sorted it.

Cheere
 
A N to E fault could cause the issues you are having.
it is the most likely fault unless of course the smart meter is within a foot (300mm) of the distribution board and then all bets are off!
 
My question really is..would a N to E fault on the non-RCD circuits cause the RCBO to trip?
No. An RCBO should only trip if there is leakage downstream of it on that circuit.
Remember the N bar is upstream from the RCBO. The circuits return N current path has to pass through the RCBO first , so the RCBO will be balanced, and won't notice any upstream N-E fault.

So circuits not on RCBOs with N-E faults should not normally affect RCBOs.
If upstream N-E faults tripped RCBO's then if you think about it every TNCS setup would have a problem.

In this case I'd quickly test the other circuits, and then believe the customer, as smart meters can most certainly cause this problem.
What make CU is it?
 
A thought. Do the RCBOs have a functional earth? Some RCBOs use the FE to monitor N-E voltage and if it rises above a threshold they trip because it 'thinks' the supply side N has become open circuit. Check then the goodness of up stream N and E conductor connections and indeed the functional earth connections. This could tie in with the client's observation about it all starting after the smart meter was installed.
 
No. An RCBO should only trip if there is leakage downstream of it on that circuit.
Remember the N bar is upstream from the RCBO. The circuits return N current path has to pass through the RCBO first , so the RCBO will be balanced, and won't notice any upstream N-E fault.

So circuits not on RCBOs with N-E faults should not normally affect RCBOs.
If upstream N-E faults tripped RCBO's then if you think about it every TNCS setup would have a problem.

In this case I'd quickly test the other circuits, and then believe the customer, as smart meters can most certainly cause this problem.
What make CU is it?
Hi thanks for the advice, it's a Hager CU.
 

Reply to RCBO tripping advice. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I’m probably going to look stupid here, but it will be worth it if I get the answer 😆, as I can’t fathom it out. I’ve never really thought of it...
Replies
22
Views
844
I have an issue with a home lighting circuit 6A RCBO provides power to 13 bulbs which randomly keeps tripping, when I say randomly it keeps...
Replies
8
Views
3K
Hi, I have just replaced an old rewireable fuseboard with a 10way consumer unit with rcbo's fitted. The issue i have is that when i connect one of...
Replies
19
Views
2K
I have a ring cct (2.5mm ) in my cabin which is protected by a 20amp RCBO. This has been in existence for over 3 years with no issues. I recently...
Replies
18
Views
1K
Ring main was on a c40 rcbo so I tested the circuit everything was fine and dropped down onto a b32, It’s quite a long circuit but only serves...
Replies
26
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock