Discuss Rcd Omission for additional socket in the UK Electrical Forum area at ElectriciansForums.net

When I was told you can add to a circuit without rcd or bonding,the only thing I can relate it to is coding no rcd as c3 rather than being c2, which I originally would have coded it as
 
Obviously best to put rcbo in but chances of it not tripping on old install...
Alex I don't think it's a good idea to try and get away with not fitting an RCD because you think it might trip due to an existing fault! o_O
 
Not saying it's a reason not to put it in,just meaning to say that it is something else to fix, rathher than spurring off socket on other side of wall,looks like it will be a case of what i was going to do and change existing socket to rcd spur and move socket to side and add addit8onal socket with both being on load side- but bedroom sockets so no real load
 

Reply to Rcd Omission for additional socket in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Evening all, If a socket circuit is not RCD protected via an RCD/RCBO and there isn't the option of fitting an additional RCD enclosure or...
Replies
20
Views
6K
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
844
2nd fixing some sockets in an office today and we were talking about high integrity earthing, I've not got a clue what the sockets are going to...
Replies
9
Views
1K
Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K
A friend's partner has an interesting fault, if it is a fault. She sets the shut down timer on the cooker and when the timer goes off (which in...
Replies
9
Views
826

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock