Discuss RCD Tripping in the DIY Electrical Advice area at ElectriciansForums.net

D

daz-18-11

Hello, I understand there are other topic with similar problems but I thought I would start a topic with my specific problem.

The RCD in our fuse box trips random when a laptop is plugged in and the switch is turned on even before the laptop is turned on, this only happens randomly and not every time. It can happen on any of the plugs in our house.

We have had an electrician visit who tested the whole house circuitry and found no problems, he tested the RCD itself which was not over sensitive so he said it was a problem with one of our appliances, he then continued to PAT the laptop chargers as well as the fridge an kettle etc. They all proved to be fine so said it was one of our appliances which couldn't be PAT tested.

So painstakingly we began to re plug in one appliance in at a time whilst then plugging in the laptop ad trying it multiple times to see what tripped he RCD, after getting towards the end we found that two alarm clocks tripped the RCD which have since been unplugged/replaced yet the problem still occasionally occurs.

Any help would be appreciated
 
The RCD is seeing the sum of all the earth leakage currents of all the individual appliances that are supplied by the socket circuits it protects. Most electronic equipment has a small amount of earth leakage and that's normal. Just because the RCD trips when the laptop is plugged in it doesn't mean the laptop is the biggest culprit.

You need to get an electrician who knows how to use more than just a PAT tester. If he suspects that one of the appliances that couldn't be tested was causing the issue he could have used an earth leakage clamp meter around the live and neutral coming from the RCD and tracked the problem down that way.
 
I would say you have a N-E fault on this side of the board. May not be on the socket circuit.

You need a competent electrician with a MFT
 
I am sure the electrician tested the board so I would imagine that an earth leakage clamp would need to be used to see what exactly the problem is.
 
Had a very similar set of circumstances recently,IR readings good,RCD ramped ok...still randomly tripped when a load was switched on. New RCD fitted no problems since.Assuming your electrician is competant with a tester (many dont have a clue) and has drawn a blank I'd swap the trip.
 
Just reading other problems on sone other forums etc. Does anybody think that it could be a problem with the wiring, such as it being pinched or the insulation damaged somewhere or is it totally unaffected due to the RCD tripping only some of the times.
 
Just reading other problems on sone other forums etc. Does anybody think that it could be a problem with the wiring, such as it being pinched or the insulation damaged somewhere or is it totally unaffected due to the RCD tripping only some of the times.

Yes!!!
 
Just reading other problems on sone other forums etc. Does anybody think that it could be a problem with the wiring, such as it being pinched or the insulation damaged somewhere or is it totally unaffected due to the RCD tripping only some of the times.

And such a problem would be revealed by the use of an insulation tester.
 

Reply to RCD Tripping in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi, I seem to have an RCD that keeps cutting the power at random times without actually tripping, if I reset it, the power comes on and will stay...
Replies
7
Views
475
Hi I am asking for help as a novice and 1st time user of this forum. Recently started to experience tripping of MCB & sometimes with the RCD at...
Replies
7
Views
554
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
My circuit panel has two banks of breakers, each bank protected by an RCD. One of these RCDs has been problematic in that it trips intermitantly...
Replies
12
Views
1K
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock