Investigating for remedial works, 2 identical but separate installations (MK Dual RCD 4+4 consumer units with 60898/B MCB's)
CU 1 RCD1 x1 >300mS, x5 >40mS, Test Button - Doesn't trip.
RCD2 x1 24mS, x5 17mS, Test Button - Trips
CU 2 RCD1 x1 >300mS, x5 >40mS, Test Button - Doesn't trip.
RCD2 x1 23mS, x5 15mS, Test Button - Trips
Identical failings for RCD 1 on both consumer units yet RCD 2 tests fine.
All other tests are as expected with good R1+R2's and Zs's
RCD's tested at output terminals, with final circuits isolated.
Thought it was more than a coincidence that the Both RCD 1's fail in the same way until I tested them myself .... any further thoughts?