Investigating for remedial works, 2 identical but separate installations (MK Dual RCD 4+4 consumer units with 60898/B MCB's)
CU 1 RCD1 x1 >300mS, x5 >40mS, Test Button - Doesn't trip.
RCD2 x1 24mS, x5 17mS, Test Button - Trips

CU 2 RCD1 x1 >300mS, x5 >40mS, Test Button - Doesn't trip.
RCD2 x1 23mS, x5 15mS, Test Button - Trips

Identical failings for RCD 1 on both consumer units yet RCD 2 tests fine.
All other tests are as expected with good R1+R2's and Zs's
RCD's tested at output terminals, with final circuits isolated.

Thought it was more than a coincidence that the Both RCD 1's fail in the same way until I tested them myself .... any further thoughts?
 
I would check the RCD is wired correctly , also neutral - earth (cpc) shorts or low impedance faults can blind the RCD
Can you swap RCD 1 with RCD 2 and check if it is the circuit or the RCD.
I had a MK RCD fail after 3 years and confirmed using that method.
If both RCD's fail on that circuit then there is a fault on the circuit - Take all the neutrals out and test again, put one neutral back in one at a time to find which circuit is at fault - switching the live MCB off does not always work as could be neutral to earth fault.
 
OP reports they don't trip on the self-test button, so it looks like they are faulty or there is something non-obvious blinding them (DC, etc).

Disconnecting the load completely and re-testing would be the obvious thing, but they might just both be from a dodgy batch.
 
Double checked (again) and RCD1's on both boards fail RCD2's on both boards pass
As previously all outgoing circuits disconnected.
Internal links (by MK) checked ok.
Came to conclusion just a coincidence, so will replace both with new.
 
Double checked (again) and RCD1's on both boards fail RCD2's on both boards pass
As previously all outgoing circuits disconnected.
Internal links (by MK) checked ok.
Came to conclusion just a coincidence, so will replace both with new.
Have you ramp tested them?
 
No but the 5x at 150mA test is way above the 30% trip value you mention in previous post, and even if it trips at X value, its still not tripping in the required time.
The 30% I was referring to was a ramp test, a 30mA RCD tripping at 36 - 40mA so quite a bit above the specified 30mA and the normally expected tripping current of 24 - 27mA

IMO the ramp test gives a better indication of the problem if the calibration of the RCD is out at the 30mA level then it is probable that the 5x test isn't injecting enough current to meet the required disconnection time
 
Last edited:

Reply to RCD's Failing in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

A few 30mA RCBO's that i have tested recently are tripping lower at x1 than they are at x5, e.g 13.1 x1 13.8 x5, I know both these results comply...
Replies
12
Views
2K
What should you do if a client has a CU that is a split board protected by 2 * 63Amp 30mA double pole RCCDs, you took Zs and tested both RCCDs by...
Replies
22
Views
2K
I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
926
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
2K
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
859

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock