Search the forum,

Discuss Real life examples of RCD fault in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
5
What’s a real life example of an imbalance between live and neutral?

For example, a faulty tumble dryer can trip a RCD on a split board - so I would assume there is an imbalance because of the difference in the magnetic flux between the Live and Neutral coils. But what would be the actual physical fault?
 
What’s a real life example of an imbalance between live and neutral?

For example, a faulty tumble dryer can trip a RCD on a split board - so I would assume there is an imbalance because of the difference in the magnetic flux between the Live and Neutral coils. But what would be the actual physical fault?
An example would be a resistance from live to cpc due to a faulty heater element or a faulty motor.
 
And another example might be a circuit unprotected by the RCD 'borrowing' a neutral from a circuit that is protected by the RCD. This is often found when older installation have RCD protection introduced for the first time.

Slightly different from the other examples, as in this case current would be straying into the RCD circuit to create the imbalance, rather than out of it.
 
further to all the comments above, one of the most common usages of an rcd (used to be) protection of a property that has no suppliers earth provided.
Therefore the installation is "TT"
any live to earth fault in this circumstance is unlikely to produce enough current to trip the over current device (unless you have an exceptionally good earth loop impedance) therefore to trip the supply to the fault, often an rcd is required to ensure safe disconnection within the required time.
 
images

This'll do it.....
 
another example would be a silly billy putting their finger or any other part of their body against a live part such as a damaged cable or table lamp with no lamp in it (exposed live is in the lamp holder)
One of the things to consider with lamp holders that have lamps missing is that there is also a neutral pin, shoving your fingers across those pins is one of the scenarios where an rcd is unlikely to help.
 

Reply to Real life examples of RCD fault in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
2K
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
400
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
868
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
My circuit panel has two banks of breakers, each bank protected by an RCD. One of these RCDs has been problematic in that it trips intermitantly...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top