Discuss Remote control of water pump in the Commercial Electrical Advice area at ElectriciansForums.net

Reaction score
0
Hi, I'm designing a wireless switching system for a cattle water trough. I'm looking for a float switch which would send a wireless signal to a receiver 300m away next to the pump and bring the pump on when required. There is line of sight between the units. At the moment the pump is switched manually but the farmer would like more control. Any suggestions?
 
What's wrong with a pressure switch controlling the pump, at the pump site and a ball valve in the cattle trough?
Water level drops, ball valve opens, pressure in pipe drops to zero, pump turns on. Trough fills, ball valve closes, pressure in pipe rises, pressure switch turns off pump.
Thanks for that Brian. As an electrician I automatically thought of an electrical solution. I'll discuss it further with the client.
 
That's the advantage of being both a sparky and a plumber, and living on a farm.
Note that the ball valve will need to WELL protected from the cattle, preferably in an enclosed compartment where they can't get at it.
An improvement to the system is to add a pressure vessel near the pump. It will prevent the pump switching on and off over short intervals.
 
Brian's suggestion is a good one but I would say it is important to check what type of pump is in use before converting to a pressure system. The presence of the ball valve will increase the head it has to deliver and the frequency of starts it has to make. Some pumps are designed for that duty, others will be subject to greater wear.

Agree with Brian that an accumulator will probably be needed, both to prevent rapid cycling of the pump as the valve closes, and also to prevent water hammer if the valve, water column in the pipe and pressure switch attempt to oscillate. A pressure switch with adjustable differential is useful here.

I have an even more radical solution for you: If the pipe run is free of sharp bends, can you blow a thin submersible cable through it for the float switch?
 
Cows are herd animals, and as such, they will ignore the trough for hours on end until one decides to have a drink. At that point, the whole lot will decide that they're thirsty and pile in, fighting and jostling for space at the trough.
The speed that five or six muzzles can lower the water level is impressive, so it's important to replenish the trough as fast as possible..
I'd suggest a low pressure ball valve to help with this - a 3/4" type if possible. This valve won't be capable of stopping the water flow on its own, because of the difference in dynamic and static pressure at the trough, but will increase the line pressure enough to trigger a pressure switch.
 

Reply to Remote control of water pump in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi having problem with my automatic sump control board the switch, for rain water pump, is not going onto auto mode when the water level reaches...
Replies
2
Views
365
  • Sticky
Ferrets are known for being small, resourceful, and incredibly clever. They can solve many problems by fitting into tight spaces and doing jobs us...
Replies
4
Views
2K
Dear Forum, I recently joined this forum, and writing for the first time. I like DIY activities, both for hobbies both to fix and repair stuff in...
Replies
1
Views
1K
I'm an electrical engineer in training so please bear with me. Basically, a bank has ordered a second 500kw diesel generator and my job is to...
Replies
3
Views
894
I am looking to switch on a Grunfos pump on a megaflow hot water tank with a wireless Rf switch I am looking for a timer which when it receives a...
Replies
1
Views
716

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock