Discuss Replacing old double light switch with new, odd wiring? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
Simple back story..

We have a double switch for our bathroom that controls the extractor fan (left switch of 2) and the bathroom lights (right switch of 2). We need to replace it as its bust basically.

Anyway i buy a Double 2 Way switch to replace it (picture below)

Anyway i take off the cover and are met with this...
IMG_5853.jpg


NO blue or brown, only seems to be 1 gang even though its a 2 button switch....

Taken off...
IMG_5855.jpg


So 2 red wires seem to be going into the top right 2 and the bottom middle 2 with the other red wire going into the top left common as well.

The earth and i’m assuming neutral are not even connected to the switch.

Now i suppose the simple question is can i use the above wiring in my new 10Amp Double 2 Way switch and if not what type of switch should i be after..?

IMG_5852.jpg

Or is it a case of simply swapping over the numbers from the old switch to the new however, on the new switch which of the common would have the 2 wires in?

Thank you for any help :)
 
Simple back story..

We have a double switch for our bathroom that controls the extractor fan (left switch of 2) and the bathroom lights (right switch of 2). We need to replace it as its bust basically.

Anyway i buy a Double 2 Way switch to replace it (picture below)

Anyway i take off the cover and are met with this...
IMG_5853.jpg


NO blue or brown, only seems to be 1 gang even though its a 2 button switch....

Taken off...
IMG_5855.jpg


So 2 red wires seem to be going into the top right 2 and the bottom middle 2 with the other red wire going into the top left common as well.

The earth and i’m assuming neutral are not even connected to the switch.

Now i suppose the simple question is can i use the above wiring in my new 10Amp Double 2 Way switch and if not what type of switch should i be after..?

IMG_5852.jpg

Or is it a case of simply swapping over the numbers from the old switch to the new however, on the new switch which of the common would have the 2 wires in?

Thank you for any help :)
If you are askng that sort of question you should be employing an electrician
 
Link the commons, and connect the LIVE in one of the common terminals, the other wires go in the two terminals marked 1 way

Thank you for replying :)

Sorry link the commons, as it is on the old one?
The live as in the red one, which red one?
Other wires the rest of the red?
Am i ignoring the black and green/yellow ones?
 
Thank you for replying :)

Sorry link the commons, as it is on the old one?
The live as in the red one, which red one?
Other wires the rest of the red?
Am i ignoring the black and green/yellow ones?
Yes, the red that was connected to the link in the old switch, SWITCH THE ELECTRICITY OFF FIRST BEFORE DOING ANY WORK
 
Last edited:
Your old switch is laid out differently to the new one.

The new one is obviously two switches .
The old one is laid out like this
16191-bcf73d266e959a5778d61d35e0fc4df9.jpg


So you'll need to transpose the wiring by 180degrees on one side.

I hope you carefully marked which red is which before you removed them...............
 
He’s got a picture :)

Your old switch is laid out differently to the new one.

The new one is obviously two switches .
The old one is laid out like this
16191-bcf73d266e959a5778d61d35e0fc4df9.jpg


So you'll need to transpose the wiring by 180degrees on one side.

I hope you carefully marked which red is which before you removed them...............
 
To simplify it for you, the red coming into the metal box that goes to "common" is your permanent live. When you flick the switch it makes the contact so the power can go back out through the other red in the "1 way" terminal to the light or fan. The small red cable on picture 2 in both commons is there to share the permanent live when switched on between the fan and light so one live wire is feeding two items.

Incoming wires

1 of red - Permanent live
1 of red - Switched live
1 of red - Switched live

As stated above hopefully you know which is which. It might be better posting this sort of thing in the DIY forum in future.:)
 
Thank you all, i’ve sorted it now and it works fine and ye i turned the electricity off! ;)

Now i have the problem of the new switch takes up more room in the box and might not been enough room in there!
 
Ha okay, i’ll leave well alone. Managed to organise it all and now back on the wall and working fine.

Out of interest why don’t they do double switch’s like my old one anymore?
 

Reply to Replacing old double light switch with new, odd wiring? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi everyone I've moved into a flat and I've decided to replace the original electric switches and sockets with white ones. I've done them all...
Replies
3
Views
849
Hi I am trying to replace my old white light switches for nice chrome ones but the wires are all red but the new switch has only l1 l2 top and...
Replies
6
Views
688
Hi all. Removed an ancient light fitting, replaced with a newer one, the light comes on but can't be turned off with the switch. It was working...
Replies
23
Views
728
First, sorry if I'm not in the correxct thread. I'm trying to replace an old switch with a WIFI switch and cannot seem to do it right. There are...
Replies
1
Views
325
Hi, I installed 6 recessed lights in my living room. I’m now up to the wiring part of the project. There is an outlet in the room that is...
Replies
1
Views
467

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock