Discuss Running a submain through distribution board, right or wrong in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Reaction score
1
Hi I've been pulled today for installing an swa glancing into the top of a header trunking then taking it through the db, saying its against the regs saying a once a main sw is off the whole db has to be dead, I can't find a reference to it,
normally I would always gland it in the bottom of the db but the cable was already installed and could only go in the top,

am am I completely in the wrong here?
thanks
 
It's impossible for the whole DB to be dead wherever the cable comes in unless the main switch is in a separate enclosure.
It is preferable for the cable to enter at the bottom, but as you say it is not always possible.
 
This is the db in question
imagepng
 
Last edited:
Bad practice, if you needed to work on the sub main, say remove or whatever, then you would need to isolate the entire board it is running through, causing disruption
 
Ud need to isolate the db anyway to work on the submain, but once the submain is in why would you need to remove it?its all ifs and buts, is there anything saying its bad practice it's certainly not prohibited and does not affect safe isolation of the board, to safely isolate the board would mean turning it of at the section panel,
 
Ud need to isolate the db anyway to work on the submain, but once the submain is in why would you need to remove it?its all ifs and buts, is there anything saying its bad practice it's certainly not prohibited and does not affect safe isolation of the board, to safely isolate the board would mean turning it of at the section panel,
Are you feeding the sub main from the board its running from? or using the board as a route
 
Last edited:

Reply to Running a submain through distribution board, right or wrong in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I'm doing a college design project and need to choose a suitable range of circuit protective devices for the whole contact. I've chosen and...
Replies
7
Views
3K
Hi all, Been browsing these forums for a while, always great to learn a new way to skin the same cat. Anyway, cut a long story short, was an...
Replies
11
Views
650
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
837
Hi there, long time lurker, first time poster here. Straight down to it.. A friend asked me to add some sockets and additional lights to a small...
Replies
0
Views
889
I have a slightly odd requirement that means I am wanting to route a 3 core 4mm SWA cable (14mm outside diameter) from outside through a cavity...
Replies
3
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock