W
wersolaruk
Anybody know a good supplier
Discuss Samill inverters? who stocks them? in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net
I'm just going to use this thread to post up a couple of thoughts / queries about Samil.
1 - Is anyone aware of any statement from Samil about the inverter not being capable of feeding DC currents into the grid? If not, and I've never found one, then a Type B RCD would need to be used if an RCD is needed.
2 - They're listed as having a power factor of 0.8lagging~0.8leading, yet G83 regulations specify a PF range of 0.95 lagging to 0.95 leading.... which begs the question for me as to whether these actually meet G83 regulations.
Has anyone checked either of these points with Samil?
needs to be in writing from the manufacturer or it's worthless really.1. I did ask the question about 18 months or so ago and remember being told that all was okay regarding DC grid injection. I can't remember if I got hold of a document backing this up. I think it was Segen that I spoke to.
2. Not noticed this. Interesting point.
yeah, but 20mA of DC leakage current is far too high for a type A RCD, hence the requirement for a type B RCD to be fitted for TL inverters unless the manufacturer specifically states that the inverter isn't capable of feeding in DC currents.I too have heard mention of high DC leakage current values with these units in the field but, in fairness, their G83 test data shows a Pass for the max DC leakage current test (20mA) and Pass for the power factor tests (0.95 lag/0.95 lead)
Where an electrical installation includes a PV power supply system that cannot prevent d.c. fault currents from entering the a.c. side of the installation, and where an RCD is needed to satisfy the
general requirements of the electrical installation in accordance with BS 7671, then the selected RCD
should be a Type B RCCB as defined in IEC 62423.
Where any doubt exists about the capability of the
inverter to prevent d.c. fault currents entering the a.c. side of the system then the manufacturer
shall be consulted.
I'm not sure if this is universal for all type A RCDs, but assuming it's at least broadly right, it's pretty obvious why a declaration about the inverter not exceeding 20mA DC injection isn't sufficient to justify their use with a Type A RCD.- from wiki
- for residual pulsating direct currents superimposed by a smooth direct current of 6 mA, with or without phase-angle control, independent of the polarity
Reply to Samill inverters? who stocks them? in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net
We get it, advertisements are annoying!
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.