ok guys im on a job at the moment and some cables are missing, i was trying to figure out the connections myself before asking anyway. (im connected most of the things up already)



anyway its a schneider damper actuator with a seperate endswitch



now am i right in thinking ill need a 6core or is the 4 core enough for the endswitch to work.



if G0 is 0v

G 24v

X1 (orange) input

Y 0-10 output



would i be right in saying it need 2 cores for the endswitch, its been quite a while since i last did a damper and i cant remember, its not an issue i can ask the engineer in the morning
 
I know nothing about damper actuators, but I do know a bit of logical thinking and basic electronics.
It appears that you have a 24V supply (+24V and gnd) plus two signals (input and output), so an endswitch could logically have one side connected to one of the supply connections, but may need its own signal connection or else it could conceivably use one of the existing signal connections and work by shorting it to either gnd or +24V.

Thinking a little bit further and making a bit of a guess then considering that the output is 0-10V then the endswitch could short the gnd supply to the output connection.
Or else a simple potential divider circuit could be arranged to connect the endswitch so that it puts a +10V signal onto the output.

Or the short version: it could be made to work on four wires.

And now you have an insight into how my mind works
 
Last edited:
I know nothing about damper actuators, but I do know a bit of logical thinking and basic electronics.
It appears that you have a 24V supply (+24V and gnd) plus two signals (input and output), so an endswitch could logically have one side connected to one of the supply connections, but may need its own signal connection or else it could conceivably use one of the existing signal connections and work by shorting it to either gnd or +24V.

Thinking a little bit further and making a bit of a guess then considering that the output is 0-10V then the endswitch could short the gnd supply to the output connection.
Or else a simple potential divider circuit could be arranged to connect the endswitch so that it puts a +10V signal onto the output.

Or the short version: it could be made to work on four wires.

And now you have an insight into how my mind works

hmm after thinking it over with a little help i think ive got it but will need to check with the engineers in the morning

bassically 24v and 0v to drive it then 0-10 input to control how much it needs to open then the spare core can be used for the endswitch (ill check with the engineer in the morning)
 

Reply to schneider damper actuator connections in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Daughter has bought a house and it has a home security system, G-Tag setup. Issue is the alarm panel displays are pixelated and you cant see...
Replies
1
Views
761
Hi guys, first time posting, please bare with me! I have an old test chart as shown in the pics that i would like to get running. Everything...
Replies
3
Views
894
I don't "do" solar, but I've been asked to comment on an aspect of a new domestic solar installation by others. There is no overload or fault...
Replies
7
Views
1K
I had a problem a couple of days ago with my boiler shutting down due to too high temperature difference between the input and output, which...
Replies
32
Views
3K
?Im struggling with adding an Alarm output to my temperature controller by Schneider Ive got everything else worked out ok The DO1 Means DIGITAL...
Replies
4
Views
835

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top