Discuss Section 2.1.2 on DTI Guide - Voc/Isc mulitpliers in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Reaction score
310
Guys,

As we know, for switches/cables/isolators etc, you need to multiply your Voc values by 1.15 and Isc values by 1.25 to calculate the relevant max values for suitable protection. However, does this apply to MPPT or Max DC voltage/current input values on inverters? Any thoughts?

Thanks

Andy
 
No, you're right Chris. I was just curious whether anyone out there actually multiplied their total Voc per string by 1.15 and then checked whether that still fell into the "MaxDC or MPPT range" details of the inverter.....

I've just checked with a certain Mr Cotterell and he confirmed that it doesn't apply to inverters per se, with the caveat that the inverter ratings must therefore still apply at -15degreeC....makes sense to me.

Cheers
 
No, you're right Chris. I was just curious whether anyone out there actually multiplied their total Voc per string by 1.15 and then checked whether that still fell into the "MaxDC or MPPT range" details of the inverter.....

Ah, I'm with you now. I've not thought about that before. It certainly isn't something that I've considered when designing a system.

with the caveat that the inverter ratings must therefore still apply at -15degreeC....makes sense to me.

At the risk of sounding stupid again. What does this mean?
 
Don't worry, I was looking at it slightly wrong I think. The MaxDC rating of the inverter input is not intrinsically linked to temp. The module's Voc temp coefficient dictates its response to temp drops in terms of voltage output. I need to run some simulations before I'm certain as to whether manually adding 15% to the Voc is roughly the same as the resulting increase in module voltage output at -15degreeC based on the module's temp coefficient for Voc (typically around -0.33/degreeC). A 40C drop in temp will result in approx 13% increase in voltage....
 
Good point. Am I right in saying that generally, overvoltage on inverters is main culprit when it comes to damaging them? Over-current not so much of an issue?
 
On the point of temp coeffcients, we check with PV-SOL - our is set to check VOC -15d as this will give a realistic high voltage, plus you know its going to start up on a cold day and keep running.
 
Yes, the -15C is the critical temperature and it's the initial over-voltage periods for some modules that can cause a problem. Also, most inverter manufacturer's specify their max Voc input values @ -15C for this reason. It's a "worst-case" scenario I guess.
 

Reply to Section 2.1.2 on DTI Guide - Voc/Isc mulitpliers in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

My brain is overheating trying to make sense of PV panel parameters and calculate the CSA of a DC feed cable to the inverter. For my 16 HL Solar...
Replies
29
Views
12K
Im getting myself all confused and want some help. Inverter is 20A max input current. I have the following: Isc 5.72 per string x 3 = 17.16...
Replies
14
Views
12K
B
Hi I have installed our first PV system, which we are using to get MCS accredited with. Its a small 5 panel system as roof space is quite small...
Replies
6
Views
8K
Graeme Harrold
G
F
Here is the second half of the long answer questions. Q 24 a) Describe how an Insulation Resistance test would be carried out on the new lighting...
Replies
5
Views
9K
Deleted member 26818
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock