Obviously depends on cable calcs, length of run, design current, presence of insulation and other de rating factors. 10mm is pretty easy as long as you dress it in tidy. Could do 2 6mm in parallel as long as they are run the same route same length but I wouldn't bother
Can't do 6mm and 2x 2.5 at all though.
 
2 x 6mm in parallel easier to connect than 1 x 10mm ? A parallel supply for a final circuit ? The mind boggles.

As gns says, 10mm is not that hard to manage, and if that's what the calcs say, that's the cable you use.
 
Its not about Cable Calcs.. im more talking about CROSS SECTION AREA

it DOSE say 10mm CSA .. what 2x6mm would be 12mm CSA ..

Thats a Darft Comment Flanders...
as for the 4x6mm to replace a 10mm .. i think you might of read things wrong there
 
Last edited by a moderator:
it DOSE say 10mm CSA .. what 2x6mm would be 12mm CSA ..

Thats a Darft Comment Flanders...
as for the 4x6mm to replace a 10mm .. i think you might of read things wrong there

It's not the daft really though is it? If you had two cables in parallel that would make 2 cables on the supply side of the switch/pull cord and two cables on the load side of the switch/pull cord making 4 cables.
 
But the comment Flanders made suggest putting 4x6mm Cables in one HOLE..

But at least the CSA would be ok.. im just shocked that some people dont see that 2x6mm CSA is 12mm CSA and would be, but BIGGER than a 10mm CSA.. I know i come from a Electronics buts basic.
 
I think I've said this before, but using 47mm deep backboxes helps, as does using a 2 gang (tall) switch if possible. As said, dress the cables well and arrange them carefully so there is room for them as you offer the switch to the box.
 
Point was that some guy on another forum had 6mm cable put in with 40A MCB that went in to the loft ..
Now with cable calcs that can drop to about 37A also the shower I think was 10K

He had a few electricians, in about it some say 6 and some say 10mm
As the 6mm was it might of been cheaper to put in a 4mm to make it up to 10mm CSA


The other thing was that lot of people didn't seem to understand that a 10mm CSA cable would be that same as 4x2.5mm CSA
What shocked me as I did think that kind of Maths was basic
 
Plus ten points for thinking outside the box. Minus thirty points for lack of understanding of the regulations and practicalities of installation.
 
Point was that some guy on another forum had 6mm cable put in with 40A MCB that went in to the loft ..
Now with cable calcs that can drop to about 37A also the shower I think was 10K

He had a few electricians, in about it some say 6 and some say 10mm
As the 6mm was it might of been cheaper to put in a 4mm to make it up to 10mm CSA


The other thing was that lot of people didn't seem to understand that a 10mm CSA cable would be that same as 4x2.5mm CSA
What shocked me as I did think that kind of Maths was basic

The reason that paralell cables are commonly used in larger circuits is that the sum of the parts is greater than the whole. If you look at the current carrying capacity of cables you will see that when the csa doubles the ccc only increases by about half. This leads to a situation where, say, 1x 70mm 4core can be replaced by 2x 25mm 4core and still have the same ccc.
However there are special requirements for parallel cables in he regulations and you need to carefully consider the protection arrangements and ensuring correct current sharing between the cables.
It is forbidden to install different size cables in parallel or for the cables to be different lengths or follow different routes.

As for the 10KW shower on a 40A mcb, it should have a running current of 42A so should be on a 45A supply to start with, however as it is a fixed load you would calculate cable size based on 42A not the rating of the OCPD as overload protection is not required.
 
Omg so this guy who has a shower installed by and electrician with 6mm cable 40A MCB going via loft.. Is OK with you guys
Sorry I must be in the wrong forum my error minus another 60


Forums ain't for me, I can't read them and tones just don't work for me...
 
Last edited by a moderator:
Point was that some guy on another forum had 6mm cable put in with 40A MCB that went in to the loft ..
Now with cable calcs that can drop to about 37A also the shower I think was 10K

He had a few electricians, in about it some say 6 and some say 10mm
As the 6mm was it might of been cheaper to put in a 4mm to make it up to 10mm CSA


The other thing was that lot of people didn't seem to understand that a 10mm CSA cable would be that same as 4x2.5mm CSA
What shocked me as I did think that kind of Maths was basic

No-one in this thread has misunderstood the maths of doubling cables up. People are disputing the advantages and practicalities of doing it in this particular case. And you should not use paralleled cables of differing csa's or type. Daz
 
this makes me think i've gone all wrong with buying a toyota hiace van, when 2 astra vans in parallel would carry the same weight.
 
A 10mm^2 conductor wouldn't need 2 * 6mm^2 in parallel for equivalent current-carrying capacity - probably more like 2 * 4mm^2.

Really parallel conductors are far more appropriate for a distribution circuit than for a final circuit, so I wouldn't be advising that approach at all.

As for other suggestions made, you cannot parallel two different cross-sectional areas of cable together as the current flow wouldn't distribute evenly.
 
This is great !!
So now an existing 6mm supply cable needs up rating to 10mm to supply a shiny new 10kw shower.
Don't bother fitting a 10mm, just run another 6mm alongside and do it on the cheap.
Well carry on cus this is the kind of thing that sorts the electricians from the semi skilled bodge up merchants.
Do what any self respecting electrician would do and fit a 10mm, and if termination is a problem get an electrician to do the job for you.
 
What about 10 x 1mm cables then? So that will be 20 in total? Using your simple infant school mathematics that would be fine.
Doesn't make it a good job though does it?

1mm has a ccc around 12/13A depending on conditions, let's say 10A for ease of maths.
So for a 40A supply you would only need 4off 1mm cables.
 
This is the way forward

Use a 2.5mm and limit the running time of the shower to 2 minutes 12 seconds using a timer.
Set the timer to re energise after 10 minutes to allow for thermal effects.

Check the calcs yourself if you don't believe me:jester:
 
Last edited by a moderator:
Use a 2.5mm and limit the running time of the shower to 2 minutes 41 seconds using a timer.
Set the timer to re energise after 10 minutes to allow for thermal effects.
Check the calcs yourself if you dont believe me. :conehead:

I believe you but don't let everyone know lol.
I am retiring to the pub for the rest of the day.

to contemplate my future
 
I have just read this and my thoughts are, why are people even talking of using more than one cable, just use the "correct" size and do it properly, anything other than that is just stupid IMO.
 
I have just read this and my thoughts are, why are people even talking of using more than one cable, just use the "correct" size and do it properly, anything other than that is just stupid IMO.

I don't think anyone is being serious petal. Maybe the OP, but even then I think this thread was possibly a joke that didn't translate to the internet very well.
 
I don't think anyone is being serious petal. Maybe the OP, but even then I think this thread was possibly a joke that didn't translate to the internet very well.

Well lets face it you either laugh or cry when reading the OP's comments.
Lets hope he IS joking, scary stuff.
 
OK how long you been in that pub Dave, I'm jealous. :wink_smile:

I haven't got near the pub yet, but it's exactly the same maths that would give you four cables with a ccc of 100A to carry a 400A supply or of 1000A to carry a 4000A supply.

The only difference being that nobody in their right mind would use paralell cables to carry a 40A supply!
 
Totally agree with Dave on this one,when you are installing large supplies sometimes you have to install large cables in parallel because the cables can become unmanageable however the same does not apply when installing a shower cable.
 
Totally agree with Dave on this one,when you are installing large supplies sometimes you have to install large cables in parallel because the cables can become unmanageable however the same does not apply when installing a shower cable.
agreed.most showers will run happily on a 2.5mm, strung over the bath and second duty as a knicker dryer.
 
All joking aside though, I think anything over 9.5kW on an instantaneous electric shower is getting a bit ridiculous and unnecessary too.

That's the fun Christmas day, when Mums cooking the Turkey, Dads watching his 65" plasma with the electric log affect fire on full blast, and the teenage daughters washing her hair in the 10.5kw shower.
Poor old 60A cut out fuse says stuff this and pop !! Merry Christmas.
 
Totally agree with Dave on this one,when you are installing large supplies sometimes you have to install large cables in parallel because the cables can become unmanageable however the same does not apply when installing a shower cable.

Count me in.
Tri-rated is another that can make those awkward break your fingers and scuff yer knuckles moments an easier option.
Have needed to fit parallel sub main runs myself on heavy installs and that's perfectly logical.
But cabling a domestic shower this way is nonsense in the extreme.
I think common sense and good electrical practice are the words of the moment with this one. ;)
 
I'd be interested to know if there's actually a reg that forbids it in the UK, I know there isn't in our domestic regs. As said already, it's common practice with cables in larger distribution networks but the logistics of ensuring identical lengths, routes and connecting a parallel cabled domestic final circuit would make it a bad idea.
 
I'd be interested to know if there's actually a reg that forbids it in the UK, I know there isn't in our domestic regs. As said already, it's common practice with cables in larger distribution networks but the logistics of ensuring identical lengths, routes and connecting a parallel cabled domestic final circuit would make it a bad idea.
BS7671 specifically permits paralleling cables, with certain provisos on cable route, type, etc. to ensure equal current sharing.
However I believe it is directed mainly toward the larger cable sizes in reality.
 
You will not need to worry in another few years because of the EU the power of vacuum cleaners are being restricted next they are going to restrict our power tools so soon your showers will be a maximum of 3KW and you will have a fine mist spray to that you reduce your need for so much water and then to round it off your bath towels will be the size of face cloths ! pmsl
 
You will not need to worry in another few years because of the EU the power of vacuum cleaners are being restricted next they are going to restrict our power tools so soon your showers will be a maximum of 3KW and you will have a fine mist spray to that you reduce your need for so much water and then to round it off your bath towels will be the size of face cloths ! pmsl

It's already in action. Companies are prohibited from manufacturing or importing any vacuums with motors above 1,600 watts and will have a further reduction in 2017 to 900 watts. What a joke lol.
 
How would you test it? As a radial or a ring final circuit?
I'm not sure the resistances in parallel are such a good idea either.
Might be a good idea to check the fire insurance.
 
A parallel circuit would be tested as a radial (possibly once for each cable), a circuit without identical conductors on the same route would be tested as a ring but must be constructed in accordance with the regulations with are fairly limiting on available design options and is generally not recommended except for the exception class of a ring final socket circuit.
 

Reply to Shower Cable in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I would like to reuse a 10mm cable to provide a ring circuit in an area. The cable is currently used for an electric shower, still connected at...
Replies
10
Views
429
Good evening all, I’m currently part way through my apprenticeship and we are working on IB, IN, IZ and IT and volt drop today. And it got me...
Replies
4
Views
484
Hi, The shower pull chord switch has snapped at my mom’s home and having unscrewed the switch I discovered a horror show(see pic). So I’ve had...
Replies
39
Views
3K
Hello, I'm not an electrician, more one of those 'competent DIYers', so probably the worst kind :) My electric shower broke, the shower firm came...
Replies
13
Views
1K
Hello All. I'm quite new to this game and gaining experience, but going well in the main. My customer wants to feed a Hob ( on island in centre...
Replies
5
Views
269

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock