Discuss Shower installed low in the UK Electrical Forum area at ElectriciansForums.net

Are we not all overthinking this?

it is a shower, fitted inside a shower enclosure.
surely just about anywhere you fit it, it has to be considered likely that it will be showered or soaked with running water.
as long as it is not in the tub where it could be immersed in standing water I would be fine with it.
 
Mira Sport Max Airboost instructions say the shower head should be so it can't dangle into the shower tray (usually achieved with a hose ring on the bottom of the riser), and the unit should be installed above the water catchment, with controls at a convenient height for the user.

Other than that, it's 'suitable for installation in the shower area', without specifying where, so I assume it's ok from that POV.
 
Where did you specify that it should be installed prior to work starting?

If that is not where you specified it to be then get them back to move it.
 
Thanks for the replies so far. I didn't specify it being at any particular height and in hindsight should have pushed for it to be rewired at first fix, it was only when a family member pointed out that they're not usually installed that low that it got me thinking. I suppose I trusted that a qualified electrician wouldn't install something in a way that wasn't safe. This is our first bathroom refurb since being homeowners and it's definitely been a learning curve.
It's not clear in the photo but the shower head can go all the way to the top of the rail, it's just set low down as it's used by young children.
The recess was put in after the first fix electrical work (it's a false wall behind) then the cold feed was added (brand new shower installation)
As I say if it's safe to use this way then I'm fine with it (also just to note it's on a separate circuit with RCD as our circuit box was full) I was just curious what others thought who might have more experience than me in this area.
 
But then the rail would be fitted lower as well for using a seat.

As it is, the head can’t be slid any higher up.
That may be so but cant see any issue with height of the shower unit itself, and with shower head that high, cant see it being sprayed from any other direction, so probably compliant with IPx3 (60deg from vertical)
Yes it could be splashed (IPx4) but again not an issue.
 
Shower enclosure is zone 1, and "certain IP rating" is required, but conditions inside the shower enclosure are not uniform. The nearer to the bottom you go, the greater the chance is that the equipment will be subjected to spray (needs IPX5), rather than just subject to splashing from all directions if mounted higher up (IPX4).
IMHO, this shower is mounted so that it could receive a direct spray from the shower head, and IPX4 is not adequate.
Thank you for corrections on that mate, I'm in my first year learning so using the forum as a tool etc very clumsy bit of advice with this one but I might remember my zones next time right haha
 
Lifted straight from the Installation guide, took me 10secs on Google....

"10. The showerhead must be directed away from the shower unit, during normal
use the showerhead must not spray directly on to the shower unit."

So it's not been fitted in accordance with the manufacturers instructions, get the electrician back to correct it, and they're also going to have to fork out for all the corrective decorative work too, so it's likely an insurance claim.

 
That being said...... which came first - the cable or the pipe?! There's possibly a plumber to blame here as well, in which case it could get messy.
 
"10. The showerhead must be directed away from the shower unit, during normal
use the showerhead must not spray directly on to the shower unit."
Dont know how you can ever ensure that with a flexible shower hose other than trying to educating the users! and stick with my comments in post#15
 

Reply to Shower installed low in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, plumber here so please be gentle (or take the p-ss ;) ), I am supposed to be installing a UV water steriliser for a customer. I have some...
Replies
16
Views
2K
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
I'm fitting one of the Apex 7S units on Friday. I'd avoided the original range after a couple of bad experiences but I figured a new model might...
Replies
6
Views
812
Hi all, new to posting but been reading for years. I inherited a house from my grandmother who passed in 2021, I intend to renovate and rent out...
Replies
97
Views
10K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock