Search the forum,

Discuss Shower pull switch opperating on load in the UK Electrical Forum area at ElectriciansForums.net

Pete999

-
Esteemed
Arms
Reaction score
17,090
A friend of a Friend asked me to go and look at a Shower that didn't work, sure enough it didn't, I took the switch off, and the connections were, to say the least a bit iffy, cores cut out, tried my best to find out who did it and after some detective work he came clean and admitted it was him, changed the switch as a safeguard, all OK until this morning, shower packed up, got there did some checks, found the switch was faulty, he said this was the second time the switch failed, he was leaving the shower switched on at the shower itself but switching it on and off via the pull cord, I reckon switching the load via the pull cord damaged the switch, any thoughts?
 
A friend of a Friend asked me to go and look at a Shower that didn't work, sure enough it didn't, I took the switch off, and the connections were, to say the least a bit iffy, cores cut out, tried my best to find out who did it and after some detective work he came clean and admitted it was him, changed the switch as a safeguard, all OK until this morning, shower packed up, got there did some checks, found the switch was faulty, he said this was the second time the switch failed, he was leaving the shower switched on at the shower itself but switching it on and off via the pull cord, I reckon switching the load via the pull cord damaged the switch, any thoughts?
What make was the pull cord Pete? Was that your article I have just read in professional electrician?
 
What make was the pull cord Pete? Was that your article I have just read in professional electrician?
MK Yes it was. I had been talking with Glenn about it, decided not to ask for the letter to be out there on the Forum, as I didn't want to upset/undermine some members, but it seems it was a daft request as many folk will put 2 and 2 together and come to the same conclusion you did when they read PE still nice to be in print at last, got a sort of book I have written about my life as a Sparks but I need to contact my old employer to get it vetted.
 
Last edited:
I had a similar problem in my home bathroom many years ago. The pull cord switch failed around two times before playing nice (prety sure it's still going to this day, touch wood). During all this the showers had to be replaced once or twice too.

I would most definetly say that using it to do the switching has caused it to fail though, I don't think there would be much design foresight for this to be used as the primary switching device.

Perhaps it is combination of its use and an underlying fault within the shower unit which has cause the failure so quickly?
 
I had a similar problem in my home bathroom many years ago. The pull cord switch failed around two times before playing nice (prety sure it's still going to this day, touch wood). During all this the showers had to be replaced once or twice too.

I would most definetly say that using it to do the switching has caused it to fail though, I don't think there would be much design foresight for this to be used as the primary switching device.

Perhaps it is combination of its use and an underlying fault within the shower unit which has cause the failure so quickly?
Yes I agree I suppose it's a luck of the draw situation, you takes your choice and hope for the best. Thanks anyway.
 
Reading up on MK 3164 (just cause I'm bored), MK list it as BS 60669-1 approved, which includes functional switching under load. MK rate that switch at 50A, so that sounds like a warranty claim?
 
Reading up on MK 3164 (just cause I'm bored), MK list it as BS 60669-1 approved, which includes functional switching under load. MK rate that switch at 50A, so that sounds like a warranty claim?
Yes I agree, can you imagine the hastle,
 
Not particularly helpful now probably but I try to only ever use the 50A round Crabtree pull switch for showers. Have found them to be so much better than other brands.
 
not so sure about the switching on load. mrs. tel has been doing it for over 10 years as she hates getting into a shower that comes on cold.
 
I don't know why people insist of using the pull cord, when a shower has a perfectly serviceable on off switch. Same people don't keep switching their electric oven on & off at the wall :mad:
 
I don't know why people insist of using the pull cord, when a shower has a perfectly serviceable on off switch. Same people don't keep switching their electric oven on & off at the wall :mad:
So would you install a Shower / Cooker without an Isolation switch then? I only ask because I had my Bathroom refurbished (only because I am old and can't do it myself) and the chaps doing the work told me I didn't need an isolation switch for my shower.
 
So would you install a Shower / Cooker without an Isolation switch then? I only ask because I had my Bathroom refurbished (only because I am old and can't do it myself) and the chaps doing the work told me I didn't need an isolation switch for my shower.

Nope needs an isolator, but they are not really functional switches IMO. There as an isolator for maintenance or safety. Bet if the shower had a digital clock on it, they wouldn't be using the pull cord all that often.

PS 'Old' more like elder statesman :)
 
Nope needs an isolator, but they are not really functional switches IMO. There as an isolator for maintenance or safety. Bet if the shower had a digital clock on it, they wouldn't be using the pull cord all that often.

PS 'Old' more like elder statesman :)
You cheeky T--t:D:eek::oops:o_O
 
I wanted to like Post 17 but the option has gone! Where's the like button? Has it gone the same way as the 'thanks' button or is it just me that can't see it ?!?

Dazburnsout.
 
Which reg states showers need a local isolator, out of interest?
I have no idea, it just didn't seem right to me , anyway I would rather leave the pull cord where it was rather than fill the hole in the ceiling up, anotherthing my Mrs would have gone Harpic if there was not a switch, it's one of her things at night makng sure everything is switched off, bless:tonguewink:
 
Nope you are quite right. There's no regulation in BS7671 to say 'when installing an electric shower for Mrs Pete999, there must be a form of local double pole isolation, with 3mm gap blah blah'.

537.3.2.1 suggests a circuit breaker is suitable means of isolation, although further guidance on this, can be obtained from Table 53.4 note (5). There's others, which I can't see the point of arguing over. Only TN supplies, think your up a gum tree with TT, but don't quote me.

134.1.1 'Good workmanship etc etc. The installation of electrical equipment shall take account of manufacturers instructions'.

I believe most, if not all domestic shower manufacturers recommend a double pole 'switch' ceiling mounted, or wall mounted in an adjacent room.

Seems like the manufactures see it as a good idea, who am I to argue?
 
I'd like MW post, but I've no longer got the ability - another loss with age? :)
I'm so used to seeing the pull switch I can't imagine not having it. Myself, I wouldn't rely on one for safe isolation, but I think manufacturers spec them for customer convenience and reassurance etc.
 
I don't know why people insist of using the pull cord, when a shower has a perfectly serviceable on off switch. Same people don't keep switching their electric oven on & off at the wall :mad:
problem there is you need to get in the shower to turn it on and for the first minute it's bloody freezing.
 
You could try one of these;

:) upload_2017-4-3_15-31-10.png
 
MK Yes it was. I had been talking with Glenn about it, decided not to ask for the letter to be out there on the Forum, as I didn't want to upset/undermine some members, but it seems it was a daft request as many folk will put 2 and 2 together and come to the same conclusion you did when they read PE still nice to be in print at last, got a sort of book I have written about my life as a Sparks but I need to contact my old employer to get it vetted.
Book as well Pete now I bet that will be interesting, how about a film with Robin Askwith in the lead roll, know what I mean;)
 
Every so often someone says a shower or cooker needn't have a local DP isolator, but as I've said before BS7671 is the minimum standard we should adhere to and it's common sense to have an easy way to switch off anything electrical without faffing about at the CU. And if say a neutral to earth fault developed on a dual RCD board at the shower you'd lose half of the installation until the cable in the shower was disconnected.
 
I would imagine the pull switch would only have a 10 or 15 amp rating ?
If this is not suficient, try using a pull switch to control a 30a contactor.
that way the contactor does all the hard work ?
 
Book as well Pete now I bet that will be interesting, how about a film with Robin Askwith in the lead roll, know what I mean;)
If it was to be one of those sort of films I don't honestly think I could keep up with Robin at my age.
 
I would imagine the pull switch would only have a 10 or 15 amp rating ?
If this is not suficient, try using a pull switch to control a 30a contactor.
that way the contactor does all the hard work ?
What a 45Amp pull switch only has a possible 10amp rating? and use a contactor? bit of a weird statement if I may be so bold.
 
15A rating? Contactor? Am I on the right thread here?
 
The only pull switchs I have seen are domestic type which are usually only 10 or 15 A at best, so I assumed thats what you were refering to. I have not seen a 45A pull switch ever. Is it suffering mechanical failure or is it clearly an electrical rating problem ?
 
The only pull switchs I have seen are domestic type which are usually only 10 or 15 A at best, so I assumed thats what you were refering to. I have not seen a 45A pull switch ever. Is it suffering mechanical failure or is it clearly an electrical rating problem ?
With respect, you should get out more then.
45A or 50A pull switches for showers are as common as muck

Screenshot 2017-04-04 07.53.54.png
 
The only pull switchs I have seen are domestic type which are usually only 10 or 15 A at best, so I assumed thats what you were refering to. I have not seen a 45A pull switch ever. Is it suffering mechanical failure or is it clearly an electrical rating problem ?
you're looking at light switches. over here we have 45A ceiling mounted pull switches for thing like showers. maybe in australia they are floor mounted. :oops:
 
Nope you are quite right. There's no regulation in BS7671 to say 'when installing an electric shower for Mrs Pete999, there must be a form of local double pole isolation, with 3mm gap blah blah'.

537.3.2.1 suggests a circuit breaker is suitable means of isolation, although further guidance on this, can be obtained from Table 53.4 note (5). There's others, which I can't see the point of arguing over. Only TN supplies, think your up a gum tree with TT, but don't quote me.

134.1.1 'Good workmanship etc etc. The installation of electrical equipment shall take account of manufacturers instructions'.

I believe most, if not all domestic shower manufacturers recommend a double pole 'switch' ceiling mounted, or wall mounted in an adjacent room.

Seems like the manufactures see it as a good idea, who am I to argue?
Every so often someone says a shower or cooker needn't have a local DP isolator, but as I've said before BS7671 is the minimum standard we should adhere to and it's common sense to have an easy way to switch off anything electrical without faffing about at the CU. And if say a neutral to earth fault developed on a dual RCD board at the shower you'd lose half of the installation until the cable in the shower was disconnected.
Just wanted to give a "like" for this post :)
 

Reply to Shower pull switch opperating on load in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, The shower pull chord switch has snapped at my mom’s home and having unscrewed the switch I discovered a horror show(see pic). So I’ve had...
Replies
39
Views
3K
This could possible have been a poll, but really just opening up for suggestions and feedback on where folks think an isolation switch for an...
Replies
12
Views
4K
Hi everyone :) my first post here. Quick background I'm a newly qualified installer of somewhat advanced years whose just starting out in the...
Replies
12
Views
1K
A friend's partner has an interesting fault, if it is a fault. She sets the shut down timer on the cooker and when the timer goes off (which in...
Replies
9
Views
873
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
323

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock