Search the forum,

Discuss Shower pullcord???? in the UK Electrical Forum area at ElectriciansForums.net

M

mickytuff

I was always under the impression that a shower pullcord or shower switch (outside the bathroom) was a requirement of a shower circuit, but i was advised today by a QS that this isnt the case as the circuit has means of isolation for maintenance purposes, ie the mcb feeding it, so my question is ........is there a regulation that states that local isolation must be present, as i thought it was.....all advice and opinions greatly recieved guys )))))
 
537.2.2. Local isolation is required. id be asking him the question why he thinks it isnt. using an MCB is fine but the distance between the board and shower are the issue
 
Where is the word local in the regs!

I think maybe if the earthing system was TT then MCB alone woould not surfice as its not double pole.

I would also look at what the manufacturer recommends!

IMOO it is best practice to fit a double pole isolator local to the shower!
 
537.2.2. Local isolation is required. id be asking him the question why he thinks it isnt. using an MCB is fine but the distance between the board and shower are the issue

nowhere in that reg requires isolation to be local.
the QS is right , you're all talking baloney.
;-)
 
i agree tony, why do you recommend/advise more of a requirement if the earthing system were TT?, in this property it was TNC-S or PME.
 
regardless of regs, on this occassion it would be bad pratice IMO not to have a double pole isolator near the shower, a pull cord is adequate for meeting this as well, imagine going straight from the breaker to the shower? would you sleep tonight ?
 
Its all about interpretation of the regs, some people try and manipulate them by saying they dont have a specific word in them, like MDJ says obviously some people sleep easier than others at night
 
Its all about interpretation of the regs, some people try and manipulate them by saying they dont have a specific word in them, like MDJ says obviously some people sleep easier than others at night

Quite so.

It should say:

All fixed electrical equipment to have 2P isolation within 2m
All kitchen items such as dishwashers, washing machines, cookers, fridges, freezers to have 2P isolation within 2M. It is NOT acceptable to have a socket concealed by the item it is supplying.
All outside circuits, power and lighting, to have 2P isolation.
 
If I do a PIR and code a shower for not having local isolation I need to identfy the regulation that is not being adhered to for the customer who is paying for the report!


If a regulation does not exist I cannot just invent one !

I agree its best practice to install a isolator!
 

Reply to Shower pullcord???? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Good evening all, I’m currently part way through my apprenticeship and we are working on IB, IN, IZ and IT and volt drop today. And it got me...
Replies
4
Views
494
Bathroom with an electric shower wired to the latest regs with a 40A MCB and RCD protection. Is the disconnection time 0.4s or 5s. Looking at the...
Replies
15
Views
3K
Hi, I've just had some electrical work completed in the bathroom; I've recently refurbished the bathroom, replacing the old electric shower with...
Replies
39
Views
8K
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K
Hi all, Been browsing these forums for a while, always great to learn a new way to skin the same cat. Anyway, cut a long story short, was an...
Replies
11
Views
778

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock