Hi all,

I have been asked to install an induction hob to an existing circuit on a 32amp mcb. The oven is a Siemens HB13NB521B rated at 20amp, the hob is a samsung NZ64H37070K rated at 32amp.

My friend is telling me that he has been told by "the man in the shop" he can run both on the one circuit. I dont believe this to be correct even with diversity.

I believe he needs to run a new circuit from his fuse board for the induction hob

Can you please help clarify if I am right or just plain stupid???

If I am stupid please be nice lol.

Many thanks,

Martin
 
be fine on the one 32A circuit. 6.0mm cable. allowing for diversity, the design current for both oven and hob together is 23A (28A if the cooker isolator has a 1363 socket outlet).
 

Reply to Single Oven / Induction hob diversity in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Evening all, I'm upgrading my kitchen electrics replacing the current gas hob for an induction hob. The oven was previously plugged into the...
Replies
6
Views
2K
Hi all, I'm getting a 32a induction hob and a 13a oven installed as part of a kitchen refurb. The existing cooker circuit is 6mm protected by a...
Replies
7
Views
2K
Hello, I’ve got an issue driving me crazy and can’t get anyone to figure it out as it’s not their issue. We had a new extension, single rear...
Replies
9
Views
1K
Hello I have two new appliances Electric oven rated at 3.95 KW Induction hob rated at 7.2 KW total of 11.15 KW Currently it is on its own...
Replies
17
Views
4K
Hi, we are replacing our old hob and cooker and I need a bit of help, to make sure all is safe. This is the oven and hob specs: AEG IKB64401FB...
Replies
0
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock