RGawley

Hi All

Has anyone come accross this yet? a friend of my fiance has opend up a Beauty Studio, she has purchased a 3 phase Sun Bed, i have not come across this yet but im more than willing to learn with your help, the stats of her Sun Bed are:
12.5KW
3 Phase
25Amps per phase (or 80Amps 1phase)
Can anyone help me by explaining what i would need to do to get it working?

Thanking you

Ry
 
Phone the DNO and ask them to upgrade supply for her salon
locate instruction manual for the sunbed
follow instruction manual to convert to single phase
decide on your cable route , type ect
pick said young lady up off the floor when she finds out the price DNO want to upgrade her supply
Pick her up off the floor and dust her down when you tell her exactly how much the materials are going to cost bearing in mnind it may end up working out at 25mm cable required and switch gear
Stand behind her to prevent her falling to the floor when you tell her how much your labour will be
 
the stats of her Sun Bed are:
12.5KW
3 Phase
25Amps per phase (or 80Amps 1phase)

Sounds high for a sun bed, are you sure this is correct info?
Can anyone help me by explaining what i would need to do to get it working?

I'm assuming you checked the supply for the premises to make sure it's sufficient to run this thing before it was purchased. If so you'll need to get an electrician to install a dedicated supply for it and connect it up. He may need to configure it for single phase or 3-phase depending on the existing CU arrangement.

If the existing power is insufficient you'll still need an electrician who will specify an upgrade required to the DNO. They'll charge you for thisI imagine, then the electrician will install an appropriate supply circuit to the sun bed as above.
 
To be honest with you there isn't a great deal you can do for a load like this. Most single to 3 phase converters are design for industrial/commercial applications and for motors.

Your only real options are to ask your local electrical supplier to provide a 3 phase installation, which could be horrendous in price, or get a smaller single phase bed
 
or get the clients to visit a warm and sunny country.
 
You don't need a converter, just wire it up single phase providing the supply will take it.

It won't have 3 phase motors in it just lamps spread arcoss 3 circuits.
 
Hi All

Has anyone come accross this yet? a friend of my fiance has opend up a Beauty Studio, she has purchased a 3 phase Sun Bed, i have not come across this yet but im more than willing to learn with your help, the stats of her Sun Bed are:
12.5KW
3 Phase
25Amps per phase (or 80Amps 1phase)
Can anyone help me by explaining what i would need to do to get it working?

Thanking you

Ry

Holy Hell! You could power the lights on Blackpool seafront on that. Are sure it's a sunbed and not a industrial kiln?
 
I’ve got a drawing somewhere in my wonderful filing system for converting a 3ph sunbed to single phase. But bear in mind the load of the sunbed added to the rest of the installation is going to be pushing the supply to the limit.

PS I’ve also got a drawing for a 2.6MW furnace for instant tanning! It’s single phase as well.
 
Just had a look at the supply last night, there is a 3 phase supply into the building but it is split up, the main supply comes into an apartment block or 8 apartments, L3 is feeding a consumer unit in her Studio and the other 2 supplies go to the apartment block, there is 4 meters, 1 main meter for the overall supply and 3 individual meters on the 3 phases. ive told her to get permission from the owner to take a 3phase supply litterly less than 10meters from the mains then into an isolator.
I have looked at the spec on the Sun bed and it is 12.5KW, aparently she won it in a compition...
 
I have looked at the spec on the Sun bed and it is 12.5KW, aparently she won it in a compition...

I would advise her to back it into the action market since she hasn't planned or budgeted for it within her business plan.

However, there is a 3-ph supply and the loading is 18A per phase. So it wouldn't be impossible to make it available.
 
You still need DNO/landlord involvement re 3 ph supply and as there are flats included in the 3 ph head i doubt they would "add it in"
 
You still need DNO/landlord involvement re 3 ph supply and as there are flats included in the 3 ph head i doubt they would "add it in"

Got on to the DNO and landlord, forms to fill and i will go from there, Thank you for all you help every1
 

Reply to Single Phase to 3 Phase in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

hi guys / girls , any advice would be appreciated, So the situation is a domestic property has a 3 phase supply , from the service head we have 3...
Replies
1
Views
300
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
627
I have a single phase stainless steel pasteuriser that has two control boxes attached to it. One box houses the control for the electronics and...
Replies
2
Views
685
Absolutely losing my brain here guys What I would like to be able to do is power our 3 phase motor on a single phase supply. Thought I had it...
Replies
3
Views
664
Hello all, I signed up here for a little help. I bought a 3 phase bandsaw and went down the rabbit hole of VFD’s etc. ‘The motor is 3 phase 400v...
Replies
9
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock