Discuss sizing SWA armour as cpc using adiabatic...... in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

B

brman

I'm doing a mod for a 3 phase circuit already installed. The only trouble is I can't work out why the existing cables are as they are so i am doubting my sums.

Existing final circuit.
3 pole memshield 2, D32 rated feeding 10mm[SUP]2[/SUP] 4 core swa with a seperate 16mm[SUP]2[/SUP] G/Y as cpc.
Measurements at the DB are max 5.6kA single phase. Zs 0.04

Cable run is about 20m so I don't think voltage drop is an issue. So why has someone fitted an additional 16mm[SUP]2[/SUP] cpc?

If I use table 54.7 I need a cpc of 10mm[SUP]2[/SUP].

If I use the adiabatic if find:
1) max Ipf across phases is 1.73x5.6=9.7kA
2) let through energy for the mem D32 MCB is 43000 at 10kA according to their specs.
3) 43000 A[SUP]2[/SUP]s and a k of 143 (assuming xlpe) gives me a minimum cpc csa of 1.45mm[SUP]2
[/SUP]
So if I wanted to use a seperate cpc I would have gone for either 10mm[SUP]2[/SUP] if using the table values or 4mm[SUP]2[/SUP] (min unprotected) if using the adiabatic.

In fact I would probably have used the pyranha nuts and the armour of the swa as 10mm2 4 core has a armour csa of 43mm[SUP]2[/SUP] which is much more than 8 times 1.45mm[SUP]2[/SUP]

Have I got my sums right as someone spent good money putting in 16mm2 so I am thinking there must have been a reason?

The only thing I can think is that using the adiabatic simply with a 5.6kA ipf and t=0.1 gives 15.4mm[SUP]2[/SUP]
but a) which select a size bigger than table 54.7 requires and b) the 5.6kA is the single phase fault current.

Plus, why 10mm[SUP]2 [/SUP]SWA? Voltage drop at 32A would be about 2.5% I think even if I used 4mm[SUP]2[/SUP]and Zs should not be a problem either, even with a type D breaker.

My job is to put a spur on this circuit but am not keep to match the cable sizes already used for no good reason.........
 
you can't use the phase/phase fault (PSCC) current in the adiabatic, as you are looking at a fault of negligible impedance between phase and Earth. (PEFC).
 
you can't use the phase/phase fault (PSCC) current in the adiabatic, as you are looking at a fault of negligible impedance between phase and Earth. (PEFC).

A good point, one which I should have realised given I am looking at sizing the cpc......:rolleyes4:

apart from that brain fart is there anything else wrong with my sums?
 
Your calculations look right using the figures you have given.
Possibilities are that it is sized as a bonding conductor or that someone had some 10mm and decided to use it or that it was originally employed for a greater load.
 
you have to use manufacturers data for the calculation as the trip time is out of range of the time/current graphs in BS7671. using that figure of 43000, your 1.45mm is correct. however, as richard said, if used as a bonding conductor, 10mm would be required. maybe they only had 16mm to hand.
 
Thanks Guys, you have confirmed I am not going mad at least ;)

I did think it might have been sized for bonding but it isn't used for it. I think the "what we had in the van" might have some truth.....

I've gone back and quoted for a new circuit on a new breaker as it is only a few quid more than messing with the old one when I take my time into account. Plus it has the bonus that I am not trying to guess what the original design intent was!
 
Rule of thumb. ....All SWA cables ((be they of PVC or XLPE insulation) from 1.5mm 2 Core, up to 95 mm 4 Core, the SWA is of a suitable CSA to be used as that cables/circuit CPC!!
 
E54 one of the lads at work tried to tell me that depending on the length of run you cannot use the SWA as the cpc. I thought he was talking rubbish and from your reply above it sounds like he was! This was a 1.5 4 core.
 

Reply to sizing SWA armour as cpc using adiabatic...... in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Firstly, please go easy as I'm still a trainee! Working on my L3 2365 I'm having trouble understanding the rationale behind adiabatics...
Replies
3
Views
829
Hi All, I'm new to Amtech/Trimble and I've been asked to review a model. I'm looking at circuits that are SWA cables using the armour and an...
Replies
4
Views
596
Hi, someone has ordered Steel Tape Armoured cable instead of SWA. Can I use this armour as a CPC the same as SWA or not and if so is there a table...
Replies
13
Views
1K
Morning All, Think I'm having a brain fart but I have a 70mm2 4 core SWA with a separate 35mm2 CPC. Earthing is TNS with main bonding...
Replies
5
Views
1K
Evening all, Having a debate with a colleague about using the SWA armouring and a separate conductor both as CPC's for a circuit. So in theory...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock