Discuss SMA 4000TL 'Insulation resistance' error in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

D

digital48

I've recently found the green light flashing and the red light on on our SMA 4000TL with the message 'Insulation resistance, check generator' on the display.

Checking the ERROROB2.CSV files I can see that this isn't the first time it has errored in this way, it has happened on odd occasions for several months. The most recent events are listed as:

SB 4000TL-20 78 2.1E+09 13/01/2017 09:06 29180 35 Outgoing Info DC Side Insulation resist.
SB 4000TL-20 78 2.1E+09 17/01/2017 09:11 29249 35 Incoming Warning DC Side Insulation resist.
SB 4000TL-20 78 2.1E+09 17/01/2017 09:11 29249 35 Incoming Error DC Side Insulation resist.
SB 4000TL-20 78 2.1E+09 17/01/2017 09:11 29249 35 Outgoing Info DC Side Insulation resist.
SB 4000TL-20 78 2.1E+09 01/02/2017 09:04 29509 35 Incoming Warning DC Side Insulation resist.
SB 4000TL-20 78 2.1E+09 01/02/2017 09:04 29509 35 Incoming Error DC Side Insulation resist.
SB 4000TL-20 78 2.1E+09 01/02/2017 09:04 29509 35 Outgoing Info DC Side Insulation resist.
SB 4000TL-20 78 2.1E+09 13/02/2017 08:55 29780 35 Incoming Warning DC Side Insulation resist.
SB 4000TL-20 78 2.1E+09 13/02/2017 08:55 29780 35 Incoming Error DC Side Insulation resist.

Is anyone able to offer an explanation and suggest what might need to be done? The installation is five years old and has 21 Canadian Solar panels on three strings.
 
Last edited by a moderator:

Hope this helps.

In essence you need to be a qualified electrician and you should follow the testing procedure in the video to identify which string (or strings) is causing the problem, which they describe as an earth fault. Then go round and check all the connections/cabling for that string.
 
it's quite common for that to happen on very cold damp winter mornings on start up, I wouldn't worry about it at that frequency. The insulation resistance value can be lowered from 1MOhm to 500Ohms to reduce the frequency of it happening, but it's not worth the call out fee at that frequency.
 

Reply to SMA 4000TL 'Insulation resistance' error in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

N
Hi, clearly a new boy with a diversity question to ask. I need to install two new circuits for NAPIT to inspect and am running into a bit of...
Replies
11
Views
2K
Engineer54
E
E
Perks of being over 60 and heading towards 70! 01. Kidnappers are not very interested in you. 02.. In a hostage situation you are likely to be...
Replies
4
Views
1K
F
Here are questions 11 - 20, I have also found the long answer section with answers so will post shortly. I apologise if there are any mistakes but...
Replies
1
Views
4K
richy8ball
R

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top