Discuss Smoke Detector Wiring in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
11
Hi All

Just a quick one. Recently had a job to install inter linked smoke detectors in the communal area of a house converted to 2 flats. Health and safety requested standard mains powered smokes with interlink.

I wired this through floors in T+E as I would in a standard domestic property, but have been pulled by another electrician stating it has to be in FP200. I have wired these from the lighting circuit (also wired in T+E) and used radio link bases so wiring it in FP200 seems pointless and pretty harsh reason to fail an EICR?

Any opinions and reg references are appreciated
 
Cables on escape routes should be avoided however not prohibited and should be kept as short as possible if it is necessary. Even if the cable were low smoke the trunking is not and I probably would have used FP. Are you being told why it is not suitable.
 
Might be wrong (Happened before) but don't the rules class a house where 2 or more people live & that are not related as a HMO ?. So although it's been subdivided inside, it may still class as 1 house as with bedsits.
Think I'd be asking the local authority what they class it as.
 
Last edited by a moderator:
From BS5839-6:2013 it sounds like what you have put in is a grade D system, this should however have been communicated to you at tender stage by the specifier. It is implied by the equipment they have told you to install but you should confirm this. If this is the case (Grade D) then BS5839-6:2013 clause 16.5 a) states that "may comprise any cable suitable for domestic mains wiring"
 
Don't think the type of system is relevant it is the wiring method on an escape route. Be interesting to know the comment on the EICR
 
Don't think the type of system is relevant it is the wiring method on an escape route. Be interesting to know the comment on the EICR
If it were a grade A, B or C then he would be using FP. The wiring method described in BS5839-6:2013 states that it should be installed as per BS7671 which doesn't ask for FP on escape routes.
 
Where non metallic cable trunking is used in escape routes suitable fire resistant means of support can be used inside the trunking
Regulation 522.11.201 so can't see the problem if pvc conduit/ trunking is used as long as it has metallic supports for the internal wiring.
 
Where non metallic cable trunking is used in escape routes suitable fire resistant means of support can be used inside the trunking
Regulation 522.11.201 so can't see the problem if pvc conduit/ trunking is used as long as it has metallic supports for the internal wiring.
Thats right. Be aware though how you fix the internal metallic supports to the building fabric. We recently had an LPCB inspection and they no longer accept plastic plug and screw as a fire resistant method of supporting anything on an escape route. They are now expecting metal rawl plugs or frame fix type screws without a plug. In tests they carried out, plugs melt and drop.

Same goes for surface P clipping or saddle clips they expect metal plugs or frame fix screws.

See attached.

IMG_3966.JPG
 
Last edited:
Nothing to do with cable fixing but flame propagating systems on an escape route, not at home to check Regs though.
 
Thats right. Be aware though how you fix the internal metallic supports to the building fabric. We recently had an LPCB inspection and they no longer accept plastic plug and screw as a fire resistant method of supporting anything on an escape route. They are now expecting metal rawl plugs or frame fix type screws without a plug. In tests they carried out, plugs melt and drop.
Self drilling masonry screws are the way forward.
 
Nothing to do with cable fixing but flame propagating systems on an escape route, not at home to check Regs though.
That regulation mentions absolutely nothing about flame propagating systems just supports.
Pvc containment is not prohibited as long as cables have metallic supports to prevent premature collapse.
Regulation 422.2.1 which can mean LSoH cables
 
Last edited:
Think we are at odds with different Regs, I get the cable fixing bit but it is the use of flame propagating materials on an escape route can't check it out at the moment.
 
Last NIC/Elecsa 'web in air' vid I watched, Cable & Stantiforth stated the use of 'plastic plugs' were still deemed to be acceptable in such situations, it was the 'clip or fixing' that has to be metal or fire resistance. Seems, their advice comes from some document or study, suggesting the plastic rawplug, would survive fire due to the surrounded concrete or brick structure.

Once again, these 'organisations & bodies' need to have some sort of joined up thinking, and stop offering conflicting guidance.

Or is it the case, some manufactures sense a marketing opportunity. :)
 
Once again, these 'organisations & bodies' need to have some sort of joined up thinking, and stop offering conflicting guidance.

I've just seen a pig flying past the window.... and IF, I say IF the IET got its act together, the "variety" of interpretations wouldn't be required..
 
That regulation mentions absolutely nothing about flame propagating systems just supports.
Pvc containment is not prohibited as long as cables have metallic supports to prevent premature collapse.
Regulation 422.2.1 which can mean LSoH cables
422.2.1 states wiring systems shall be non-flame propagating. It is there in black and white.
 

Reply to Smoke Detector Wiring in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I need your help please once again in tracing a fault. Am DIY but not clueless. Converting former kitchen into 2 rooms: bathroom and laundry. The...
Replies
24
Views
2K
Hi all Recently we've been having a few issues with smoke and heat detectors.. been fitting them for years and years now mostly without any...
Replies
14
Views
2K
Not come across this before, so would like some help, please. I went to install smokes and heat alarm (to new Scottish regs) in a fairly modern...
Replies
2
Views
1K
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
Good evening all 3 buildings : 1 Gf flat and 1St fl flat year 1915 2nd 6 flats year 1980 3rd cottage year 1900 They are separate buildings...
Replies
29
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock