Hi All

Just a quick one. Recently had a job to install inter linked smoke detectors in the communal area of a house converted to 2 flats. Health and safety requested standard mains powered smokes with interlink.

I wired this through floors in T+E as I would in a standard domestic property, but have been pulled by another electrician stating it has to be in FP200. I have wired these from the lighting circuit (also wired in T+E) and used radio link bases so wiring it in FP200 seems pointless and pretty harsh reason to fail an EICR?

Any opinions and reg references are appreciated
 
Cables on escape routes should be avoided however not prohibited and should be kept as short as possible if it is necessary. Even if the cable were low smoke the trunking is not and I probably would have used FP. Are you being told why it is not suitable.
 
Might be wrong (Happened before) but don't the rules class a house where 2 or more people live & that are not related as a HMO ?. So although it's been subdivided inside, it may still class as 1 house as with bedsits.
Think I'd be asking the local authority what they class it as.
 
Last edited by a moderator:
From BS5839-6:2013 it sounds like what you have put in is a grade D system, this should however have been communicated to you at tender stage by the specifier. It is implied by the equipment they have told you to install but you should confirm this. If this is the case (Grade D) then BS5839-6:2013 clause 16.5 a) states that "may comprise any cable suitable for domestic mains wiring"
 
Don't think the type of system is relevant it is the wiring method on an escape route. Be interesting to know the comment on the EICR
 
Don't think the type of system is relevant it is the wiring method on an escape route. Be interesting to know the comment on the EICR
If it were a grade A, B or C then he would be using FP. The wiring method described in BS5839-6:2013 states that it should be installed as per BS7671 which doesn't ask for FP on escape routes.
 
Where non metallic cable trunking is used in escape routes suitable fire resistant means of support can be used inside the trunking
Regulation 522.11.201 so can't see the problem if pvc conduit/ trunking is used as long as it has metallic supports for the internal wiring.
 
Where non metallic cable trunking is used in escape routes suitable fire resistant means of support can be used inside the trunking
Regulation 522.11.201 so can't see the problem if pvc conduit/ trunking is used as long as it has metallic supports for the internal wiring.
Thats right. Be aware though how you fix the internal metallic supports to the building fabric. We recently had an LPCB inspection and they no longer accept plastic plug and screw as a fire resistant method of supporting anything on an escape route. They are now expecting metal rawl plugs or frame fix type screws without a plug. In tests they carried out, plugs melt and drop.

Same goes for surface P clipping or saddle clips they expect metal plugs or frame fix screws.

See attached.

IMG_3966.JPG
 
Last edited:
Nothing to do with cable fixing but flame propagating systems on an escape route, not at home to check Regs though.
 
Thats right. Be aware though how you fix the internal metallic supports to the building fabric. We recently had an LPCB inspection and they no longer accept plastic plug and screw as a fire resistant method of supporting anything on an escape route. They are now expecting metal rawl plugs or frame fix type screws without a plug. In tests they carried out, plugs melt and drop.
Self drilling masonry screws are the way forward.
 
Nothing to do with cable fixing but flame propagating systems on an escape route, not at home to check Regs though.
That regulation mentions absolutely nothing about flame propagating systems just supports.
Pvc containment is not prohibited as long as cables have metallic supports to prevent premature collapse.
Regulation 422.2.1 which can mean LSoH cables
 
Last edited:
Think we are at odds with different Regs, I get the cable fixing bit but it is the use of flame propagating materials on an escape route can't check it out at the moment.
 
Last NIC/Elecsa 'web in air' vid I watched, Cable & Stantiforth stated the use of 'plastic plugs' were still deemed to be acceptable in such situations, it was the 'clip or fixing' that has to be metal or fire resistance. Seems, their advice comes from some document or study, suggesting the plastic rawplug, would survive fire due to the surrounded concrete or brick structure.

Once again, these 'organisations & bodies' need to have some sort of joined up thinking, and stop offering conflicting guidance.

Or is it the case, some manufactures sense a marketing opportunity. :)
 
Once again, these 'organisations & bodies' need to have some sort of joined up thinking, and stop offering conflicting guidance.

I've just seen a pig flying past the window.... and IF, I say IF the IET got its act together, the "variety" of interpretations wouldn't be required..
 
That regulation mentions absolutely nothing about flame propagating systems just supports.
Pvc containment is not prohibited as long as cables have metallic supports to prevent premature collapse.
Regulation 422.2.1 which can mean LSoH cables
422.2.1 states wiring systems shall be non-flame propagating. It is there in black and white.
 
Fresh back from a few days away, I'm tempted to ask "so would normal cable be flame propagating ? "
Fire rated cables I get, but is that the same as non flame propagating ?
May need to duck off back to Heidi Land :)
 
Think people are so blinded by Am 3 and fire resistant fixings they ignore the requirements for cable systems on escape routes and T&E most certainly would not comply even if it were fixed with indestructible clips. Comment frequently when doing FRAs on this type of thing.
 
Reading that 422.2.1, towards the end it does say for BD2/3/4 the wiring systems shall be fire rated... (edit : just read Ian post #24 )
I did set fire to a cable to see what happened - not as bad as I'd hoped thought with the cable self extinguishing within about 10sec. Not surprising it failed IR testing after meeting Mr Rothenberger. Now for the pics :)

IMG_0637.JPG
 
Reading that 422.2.1, towards the end it does say for BD2/3/4 the cables shall be fire rated...
I did set fire to a cable to see what happened - not as bad as I'd hoped thought with the cable self extinguishing within about 10sec. Not surprising it failed IR testing after meeting Mr Rothenberger. Now for the pics :)

View attachment 36346
Try that with LSOH cable which is non fire propagating and will not give off the fumes standard twin & earth will
 
FP200 not used for smoke detectors- C2

Had no regulation reference or anything
I would contact them and ask their reasons. A Grade D system does not need fire resisting cable unless the requirements of BS7671 could only be met by doing so. I find it unlikely, though not impossible the reason is for an inappropriate wiring system on an escape route. More likely they have misread BS5839-6 or confused it with BS5839-1, the fact they have given a Code 2 is neither here nor there and it would be interesting to know why they have picked up on it to resolve your problem.
 
Reading that 422.2.1, towards the end it does say for BD2/3/4 the wiring systems shall be fire rated... (edit : just read Ian post #24 )
I did set fire to a cable to see what happened - not as bad as I'd hoped thought with the cable self extinguishing within about 10sec. Not surprising it failed IR testing after meeting Mr Rothenberger. Now for the pics :)

View attachment 36346

fire will tend to travel upwards rather than down so you have it biased towards self extinguishing there. If you did it again but set fire to the bottom of a vertical section of cable you might get it to burn a bit longer.
 
We are going off in a tangent here..lol
Domestic fire detection must meet BS5839 part 6 & BS 7671. Grade D can be wired from the consumer unit or from a local light fitting, in normal T&E. If specified then LSOH. As with emergency lighting, the units contain back up batteries. So the cable is sacrificial. The units also require a screwdriver to remove from the base, giving total isolation from mains, complying with the lockable isolation rule. Grading such as A,B,or C utilize a central psu, or control panel so the cable now becomes and issue to supply as long as possible. So here FP or Pyro would be required.
 

Reply to Smoke Detector Wiring in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I need your help please once again in tracing a fault. Am DIY but not clueless. Converting former kitchen into 2 rooms: bathroom and laundry. The...
Replies
24
Views
2K
Hi all Recently we've been having a few issues with smoke and heat detectors.. been fitting them for years and years now mostly without any...
Replies
14
Views
2K
Not come across this before, so would like some help, please. I went to install smokes and heat alarm (to new Scottish regs) in a fairly modern...
Replies
2
Views
1K
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
Good evening all 3 buildings : 1 Gf flat and 1St fl flat year 1915 2nd 6 flats year 1980 3rd cottage year 1900 They are separate buildings...
Replies
29
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock